The boiler was installed about 9 months ago. It replaced a conventional potterton and was 'dropped in' on existing pipework - the pipework is like most old systems - extended and fiddled with over time.
Problems existed from day 1 with reliable operation of the system. Over time the pump and the diverter valve were replaced. System would work for a day or two and then back to unreliable operation with lockout occuring - boiler indicated incorrect or reversed flow. A day of detailed work found two faults, - 1 with the cylinder stat and 2 with the return from the DHW cylinder being connected to the boiler flow. These errors were corrected - all was fine for about 3/4 weeks.
Whilst the parents on holiday the son reported that the boiler had stopped creating DHW Investigation shows boiler not firing up if only DHW is set on with programmer. If Ch is active as well, or CH only, boiler fires up fine.
As a test I set DHW on, manually operated diverter valve to mid position and the boiler then ran without problem - however having CH on when outside temp is 25C is not nice!
The return pipework from the DHW tank to the boiler starts off in 22mm, reduces to 15mm and then joins CH return at boiler - the CH return is 22mm. Could this create a problem in circulation. ??
I ask this becaues when the boiler fails to start with DHW only being demanded, the circulation pump is running but I cannot feel any difference in temp at the boiler between the flow and return pipework. Occasionaly the boiler will light for around 20 seconds and then shut down. An occasional click is heard but the boiler doesn't light
I am of a mind to replace this section of 15mm pipe with 22m but is is going to involve taking out a bath because of the way the pipework has been installed and then the bathroom rebuilt at a later date. Thoughts appreciated
I have checked out wiring and operation of diverter valve/pump/cylidner stat and thermostat as detailed in another post on this forum (CH programmer or motorised valve t-8369) and confirm wiring and operation of valves etc is correct.
Problems existed from day 1 with reliable operation of the system. Over time the pump and the diverter valve were replaced. System would work for a day or two and then back to unreliable operation with lockout occuring - boiler indicated incorrect or reversed flow. A day of detailed work found two faults, - 1 with the cylinder stat and 2 with the return from the DHW cylinder being connected to the boiler flow. These errors were corrected - all was fine for about 3/4 weeks.
Whilst the parents on holiday the son reported that the boiler had stopped creating DHW Investigation shows boiler not firing up if only DHW is set on with programmer. If Ch is active as well, or CH only, boiler fires up fine.
As a test I set DHW on, manually operated diverter valve to mid position and the boiler then ran without problem - however having CH on when outside temp is 25C is not nice!
The return pipework from the DHW tank to the boiler starts off in 22mm, reduces to 15mm and then joins CH return at boiler - the CH return is 22mm. Could this create a problem in circulation. ??
I ask this becaues when the boiler fails to start with DHW only being demanded, the circulation pump is running but I cannot feel any difference in temp at the boiler between the flow and return pipework. Occasionaly the boiler will light for around 20 seconds and then shut down. An occasional click is heard but the boiler doesn't light
I am of a mind to replace this section of 15mm pipe with 22m but is is going to involve taking out a bath because of the way the pipework has been installed and then the bathroom rebuilt at a later date. Thoughts appreciated
I have checked out wiring and operation of diverter valve/pump/cylidner stat and thermostat as detailed in another post on this forum (CH programmer or motorised valve t-8369) and confirm wiring and operation of valves etc is correct.