pressure building up after heating comes on

Joined
3 Mar 2006
Messages
23
Reaction score
0
Country
United Kingdom
Same old problem with POTTERTON PUMA 80 e.THE PRESSURE BUILDS UP ONCE THE HEATING COMES ON AND KEEPS RISING TILL THE PRESSURE VALVE RELIEVES IT. ANY COMMENTS WELCOME!! :evil:
 
Sponsored Links
You would not have to search very far to see that this is a problem with the expansion vessel.

This is why we ask that you read the FAQ first as most common problems are covered.

Look in FAQ at the top please!

Tony
 
Sponsored Links
I am sure that you have!

However I am also sure that you have NOT done it in accordance with the instructions.

Please do it as instructed!

Tony
 
HAVE REPRESSURISED TO THE LETTER AND IT STILL RISES. IT'S NOT THE FILLING LOOP AS IT ONLY RISES WHEN THE HEATING COMES ON
 
.THE BRAIDED HOSE FROM THE EX VESSEL WAS BLOCKED AT ITS CONNECTION AND AFTER 6 MONTHS IT WORKING PROPERLY AGAIN!!!

THANKS TO HARROGATE!!!!!
 
If it has been correctly repressurised then the communication pipe from the boiler is blocked.

But you seem to know that already!

Tony
 