Ah. that must be it - my mistake.Quite possible. Copper superconducts at 0 Kelvin and the OP does say that the boiler is on the faulty circuit. I believe Copper Oxides exhibit superconductivity at higher temperatures, so older cables would help.
I really don't know for sure, but I had assumed that a standalone IR tester (I've never owned one) was just a standalone IR tester. To be able to measure very low resistances as well as IR, it presumably would have to contain some separate, different, technology - since using 500V to measure very low resistances would result in some very interesting currents - IR testers themselves 'cutoff' below a certain resistance, for that reason.Oh. I thought they all did. I may be wrong.I didn't think that (m)any 'standalone' IR testers had such a facility?
I'm a bit confused. If, as I have 'assumed' (I know!), he disconnected the circuit in question from the CU and then found no continuity between that (disconnected) circuit and any other circuits, could he not then be certain that there were no 'cross-connections' (which is what I'm assuming was the point of the exercise)?No. I meant, whilst looking for a fault, how can he be certain.
Thanks for confirming.Thanks John for making mostly correct assumptions
It is certainly the circuit which has produced the lowest IR readings, but they really are not low enough to explain an RCBO trip. Even with a full 230V across it, the current though a 34 MΩ 'leak' would only be about 0.007 mA - hardly enough to trip a 30mA RCBO.Fuse--------Circuit--------------- LN------------NE------------LE
6 -----------Gnd Ring ------------ 390 ---------- 34 ----------- 420
The results above indicate the Gnd floor 'NE' is suspect - but cannot see anything. By the way all wiring is exposed in basement so didn't have to lift floor boards to visually inspect.
He said that the IR measurements were undertaken with a 500V IR tester, the multimeter only being used for the ring 'continuity' measurement.Are you sure it is Mega ohms? Most continuity meters go up to 2000 ohms.
I agree - but, as I said, I don't think it makes any sense to suggest that all those recently-presented IR readings were in ohms, rather than Mohms - that just can't be the case!No, but there are inconsistencies in the thread.
Who knows - it's mysterious. The vacuum cleaner itself clearly cannot be the source of 'leakage', since (IIRC) it's only '2-core' - all it really could be doing (particularly at start-up) would be to 'reveal' a N-E fault elsewhere by putting a transiently large load on the circuit. The fact that switching on the computer socket, but not the computer, (thereby probably exposing the installation to capacitors at the power input to the computer PSU) can cause trips does, indeed, suggest that there is a pre-existing total leakage quite close to 30mA - but goodness knows (on the basis of what we've been told) where!Are we then to assume that all the circuits are fine and the fault is to another earth source? or - "It always happens with vacuum (1320W). But remember not on upstairs circuit.
Kettle (2000W) plus microwave (1000w) no effect.
But sometimes the microwave on its own causes problem.
Sometimes computer (600w) switched on at socket but not powered up causes problem.
Then sometimes it just flips without any noticeable appliance change - say noticeable as the boiler may have fired up."
just accumulative leakage?
I hope you're right - but if 'those very same low IR results' your talking about are those ones in tens of MΩ, that really shouldn't be enough to trip an RCBO.I have fingers crossed - think I have found it.
There is a fused spur outlet which has not ben used for about 15 years (and I had almost forgotten about). Had some panelling put in recently and guess what must have nailed through the cable. Luckily the outlet is actually on a spur (not directly on the ring). So I've disconnected t. On testing the cable to the fused outlet (now hidden behind panelling) I get those very same low insulation results.