Agree entirely. But then as I mentioned in another thread recently, the whole SP vs. DP for TN vs. TT issue makes so sense to begin with.
Yes, you did, and I think that I more-or-less agreed with you at the time. However, having now thought a bit more about it, I think it probably does make some sense in relation to TT vs.TN-C-S, but less (if any) sense with TN-S vs. TT ....
With TN-C-S, no matter what potential the neutral supply may have relative to true earth (e.g. due to supply-side faults in the ‘right’ place), in the absence of faults
within the installation, neutral will always be about the same potential as the installation's CPCs and any bonded metalwork, so there should be no risk to someone working on a circuit which had only had its L isolated. However, with TT, if neutral acquires a high potential relative to true earth, there will also be roughly that same pd between neutral and CPCs/bonded metalwork. Isolation of neutral therefore theoretically becomes desirable - that is, if one feels that the probability of someone working on an isolated circuit at the very time that there is a high neutral potential is something other than 'vanishingly small'!
However, as I see it, with TN-S, there is also a similar theoretical risk (of a high pd between neutral and CPCs/bonded metalwork) in the event that the supply neutral broke at the ‘right’ place (since CPCs and bonding are not connected to N within the premises, but may have a path to true earth via the DNO's earth conductor and/or bonded e-c-ps) – so there might again be a case for advising DP isolation to ‘cover’ the very improbable scenario postulated.
In other words, albeit we’re talking about a very low risk, I think I can see an argument for DP isolation with TT but not with TN-C-S, but it seems to me that the argument for DP isolation would also apply to TN-S.
When we discussed this before, I think we considered an apparently ‘anomolous’ situation in which, say, two adjacent properties have the same TN-C-S supply but that one of them ignored the DNO's earth and TTd their installation - with one 'requiring' DP isolation and the other not. However, I now don’t think that’s really an anomoly. If both premises were ‘enjoying’ a high neutral potential, there would be a high N-CPC pd in the TT house but not in the TN-C-S one.
... or maybe my ‘second thoughts’ are even more flawed than my original ones? I have to say that 'first thoughts' are often right and 'corrected ones' wrong
Kind Regards, John.