I've inherited a house with a TT system and a spattering of Single Pole RCBOs on the ring main circuits (previous occupant apparently had them installed along with a new panel as an "upgrade"), and I can tell you exactly why they are a bad idea.
The whole point of RCBOs is to give you greater discrimination than you get with the 1 or 2 RCDs in a split load panel.
With a TN-C-S system this is exactly what you get. One feed has a fault, the single pole RCBO trips the circuit, phase is removed, the other circuits aren't impacted.
For a TT system, the high earth impedance means you histrorically _had_ to have a 100mA type S (delayed) RCD on the incomer otherwise high current MCBs won't open in the event of a phase-earth fault.
With a classic split load board the downstream (almost certainly dual pole) 30mA RCDs will trip on a fault and the 100mA type S won't. This is the case for both neutral and phase faults.
With single pole RCBOs and TT, you get discrimination on phase-earth faults, but not neutral-earth faults. Touch a neutral to ground with RCBOs & a TT system protected with a 100mA type S (or in my case have condensation in an outbuilding between neutral and earth in a light fitting) and both the RCBO and type S trips plunging you into darkness in the middle of the night
If it was a split load board, the 30mA RCD would have disconnected both phase and neutral, and the rest of the install would have stayed on.
This is reflected in the 17Ed regs and on-site guide which show split-load (with 100mA type S on the incomer) or all circuits being RCBOs (assumed SP because 1 mod wide) being suitable for TT, but not mixed type S and single pole RCBOs.
Fyi, I'm currently trying to decide whether to buy more RCBOs or move back to split panel.