Good to see you. I hope all is well with you and yours and am grateful for your input into this discussion.
I would go back to the start of the thread, as it has meandered. 522.6.202 refers to 3 terms which create the zones. The terms are defined in Part 2 as follows:
1. Point - A termination of the fixed wiring intended for the connection of current-using equipment.
2. Accessory - A device, other than current-using equipment, associated with such equipment or with the wiring of an installation.
3. Switchgear - An assembly of main and auxiliary switching equipment for operation, regulation, protection or other control of an electrical installation.
Item 1 covers a cable sticking out of a wall to connect a shower (for example).
Item 2 covers a flex outlet plate to connect an oven (for example).
Item3 covers a socket to allow a home-owner plug in their TV (for example).
All totally agreed, other than that I think I would personally regard a socket as "2" (an accessory), rathre than "3" (switchgear)
As an electrician, the requirement is then to run the cable horizontally or vertically to the item.
Indeed so - but all of us involved in this discussion have always known all that
The question I asked (spun off from another thread) relates specifically to large items of current-using equipment, the original thread having been about large illuminated mirrors fixed to a wall such that they could not be removed 'without use of a tool' (and with the means of connection to the electricity supply not visible).
In that situation, which, if any, of the three things specified (your 1, 2 & 3) would the item represent (i.e. would it create a 'zone' per 522.6.202?) , and what would be the dimensions of the zones it created.
One final comment is that there is no such thing as a 'safe zone', 'prescribed zone', preferred zone' or ' zone of protection'.
Totally agreed. That is why I always try to remember to put "safe zone" in quotes (I often {grudgingly!} use the term, since it's the terminology that so many others use) or. preferably, refer to them as 'permitted zones' (permitted to bury cables).
This whole thread has been confused (I guess your 'meandering') since, despite my repeated attempts to get them back 'on question', people have been persistently talking about where 'a man with a drill' should consider cables might be (in what to him,/her would be 'dangerous zones'), whereas I have, from the start, been asking very specifically about where, per BS7671, one is
permitted to bury cables when the only visible 'clue' is a large current-using item fixed to the wall. They are different questions.
Kind Regards, John