Sime super 105 mk2 pressure.

Joined
3 Jul 2006
Messages
204
Reaction score
5
Country
United Kingdom
Daughter moved into a house with a Sime super 105 mk2 boiler. she had to have some plastering work done, so I removed a radiator. Whilst I was there I checked the boiler and saw water pressure was almost zero. Not being familiar with the boiler I couldn't see where the filling loop was, so said I'd look for the manual on the web. Meanwhile two days later she phoned me to say the pressure had suddenly gone up to 3 and the pressure relief valve had opened. I went round to have a look and sure enough it was at 3. I bled a rad to relieve the pressure and asked her to keep an eye on the pressure. I can't understand how the pressure has increased unless the filling valve is not fully closed. Any ideas on this?
 
Sponsored Links
If the boiler is continually at 3bar whether it is operating or not then either the filling loop is passing or the DHW heat exchanger is pinholed causing mains water to mix with central heating water
 