It suggests that a lack of discussion at higher levels particularly in the case on CNE which is very prone to loss of neutral/earth.
If you think of cable design, the original 4core was: -
4 cores (copper and later aluminium) with paper insulation
an outer belt baper insulation surrounding the cores
a lead sheath
a layer of hessian soaked in bitumen
2 laters of steel tape (though SWA is used)
another layer in hessian
When PME came legal the design changed, initially 3 designs were specified by the industry with them being spread amongs the 'Leccy Boards for trial
They all had 3 aluminium cores with paper insulation, then the differences began, with a choice of copper or aluminium stranded N/E or a solid aluminium sheath.
All covered by a PVC sheath.
It was discovered over time that if the PVC was damaged aluminium sheaths could then corrode from ground water and the N/E would be lost, hence the start of the famous "Neutral Fault"
The companies using the solid aluminium sheath were by far the worst affected (guess what one I work in).
I would say we have in to double figures of these a year and it is a huge concern.
From the older designs apart from theft we don't have any!
Yet the non PME is seen as the greater hazard
Go Figure
I suspect that it comes from EU concerns, as out of the UK concern about correct polarity is not the issue we have, so treating the neutral as live makes sense from that point of view
(it was the same with core colours for 3 phase, we were, I have been told, pretty much the only country that wanted seperate colours for the individual phases. The rest of the EU was happy to have 3 brown and 1 blue as they were used to sort phase rotation on an individual basis!)
If you think of cable design, the original 4core was: -
4 cores (copper and later aluminium) with paper insulation
an outer belt baper insulation surrounding the cores
a lead sheath
a layer of hessian soaked in bitumen
2 laters of steel tape (though SWA is used)
another layer in hessian
When PME came legal the design changed, initially 3 designs were specified by the industry with them being spread amongs the 'Leccy Boards for trial
They all had 3 aluminium cores with paper insulation, then the differences began, with a choice of copper or aluminium stranded N/E or a solid aluminium sheath.
All covered by a PVC sheath.
It was discovered over time that if the PVC was damaged aluminium sheaths could then corrode from ground water and the N/E would be lost, hence the start of the famous "Neutral Fault"
The companies using the solid aluminium sheath were by far the worst affected (guess what one I work in).
I would say we have in to double figures of these a year and it is a huge concern.
From the older designs apart from theft we don't have any!
Yet the non PME is seen as the greater hazard
Go Figure
I suspect that it comes from EU concerns, as out of the UK concern about correct polarity is not the issue we have, so treating the neutral as live makes sense from that point of view
(it was the same with core colours for 3 phase, we were, I have been told, pretty much the only country that wanted seperate colours for the individual phases. The rest of the EU was happy to have 3 brown and 1 blue as they were used to sort phase rotation on an individual basis!)