That's the purpose - to equalise potential under fault conditions.
What about to equalise potential in the case of an accident ?
A metal sink with the taps fitted into the work top and a plastic drain pipe. As I read it there is no need for this to be bonded ( or "earthed" ) as it cannot introduce any potential into the equipptential zone.
The accident is a double insulted hand held food mixer is dropped into the sink when the sink has water in it deep enough to cover the food mixer and the mixer is plugged in and the socket switch is on.
No safety device will operate. There is no path from the sink to the CPC so there is no "earth" leakage so the RCD has no reason to operate. Unless the water is extremely conductive it is unlikely even a 3 amp fuse will blow.
We have a sink with a potential somewhere between neutral and live. The actual voltage depends on the ratio of areas of live parts and areas of neutral parts in contact with the water.
Touching the sink and at the same time any "earthed" item ( direct via CPC or indirect via bond to an "earthed" item will result in a serious electric shock. Bare feet on a damp floor could also provide a second point of contact sufficient for a severe shock. With luck the current through the person may be enough to trip an RCD if fitted.
If the sink was bonded ( or "earthed" ) then the RCD would (should) have operated within seconds of the mixer entering the water. And even in the fault ( accident created ) earth leakage current was not enough to trip the RCD there would be no risk of serious electrical shock as the sink would be prevented from having a potential signicantly different from any other "earthed" or bonded items in the vicinity.
Doesn't common sense apply here ? Or does blind observance of "the regulations" which no longer require sinks to be bonded become interpreted to mean kitchen sinks "must not be bonded".
And consider when the fault is a fault that has driven the CPC above ground potential. If the sink is not bonded then any electrical leakage through damp work surface and damp walls to real ground could mean the sink is grounded with an impedance low enough that someone touching the sink and an "earthed" or bonded item ( no longer at or near ground potential ) will receive a mild to medium shock. In this case because the potential difference is between true ground and the CPC and does not involve live or neutral the RCD will not operate no matter how high the current through the person's body.