S
sjwkmje
Hi All,
Asked to fit a supply to a large APC 4u rack mount UPS. It requires a 16A BS4343. I will be fitting a MK commando switched blue 16A surface mount socket next to the network rack. Its about 10 meters from a CU so cabling is fine in 2.5mm t+e with 4mm g/y to bond the cab from the earth bar inside the cu. Problem here is 17th edition, requirements for RCDs 522.6.7.
The cable will not be at a depth of 50mm due to it been a dry line partition wall. The unit is surface mount but the cable will go inside the wall and drop into the floor and back up to the cu the other side of the room.
I would not want to fit the UPS that will be feeding network servers and other equipment from an RCD supply. I would rather fit a c type 16a MCB.
Do I need to run the cable on the surface to avoid RCD projection or run it inside galv ducting inside the wall? Of course the galv ducting will have to be earthed along its entire length.
Any ideas?
Adam
Asked to fit a supply to a large APC 4u rack mount UPS. It requires a 16A BS4343. I will be fitting a MK commando switched blue 16A surface mount socket next to the network rack. Its about 10 meters from a CU so cabling is fine in 2.5mm t+e with 4mm g/y to bond the cab from the earth bar inside the cu. Problem here is 17th edition, requirements for RCDs 522.6.7.
The cable will not be at a depth of 50mm due to it been a dry line partition wall. The unit is surface mount but the cable will go inside the wall and drop into the floor and back up to the cu the other side of the room.
I would not want to fit the UPS that will be feeding network servers and other equipment from an RCD supply. I would rather fit a c type 16a MCB.
Do I need to run the cable on the surface to avoid RCD projection or run it inside galv ducting inside the wall? Of course the galv ducting will have to be earthed along its entire length.
Any ideas?
Adam