SWA Cable connecting to normal flex via junction box

Discussion in 'Electrics UK' started by widgles, 3 Apr 2007.

  1. widgles

    Joined:
    30 Mar 2007
    Messages:
    3
    Thanks Received:
    0
    Location:
    Essex
    Country:
    United Kingdom
    I'm not electrical minded I am ony ask on behalf of someone without computer access.

    As the title say we need to connect the SWA cable to normal flex & plus via junction box so the power runs through (as you can't put a plug on SWA)

    SWA cable has 3 wires : Brown, Black & Grey
    Flex: Brown, Blue and Gwn/Yw

    I've tried to look up the wire colours on the computer but have got confused looking at the new regulations colours etc

    We understand the colour on the normal flex (Live, Neutral & Earth) but what are they on the SWA? (we have earthed the SWA cable using the correct Glands)

    Any advice would be much appreciated.
     
  2. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    Are you entirely sure you know what you are doing? I take it by using SWA it is going underground outside? Are you aware of part P of the building regs? I don't mean to put you down, just that if not done correctly, this can be very dangerous.
     
  3. sm1thson

    Joined:
    5 Sep 2005
    Messages:
    829
    Thanks Received:
    0
    Location:
    Hull
    Country:
    United Kingdom
    SWA-Junction box-Flex-Plug
    something doesnt sound right, can you explain more what you are doing and why?
     
  4. widgles

    Joined:
    30 Mar 2007
    Messages:
    3
    Thanks Received:
    0
    Location:
    Essex
    Country:
    United Kingdom
    It's not me doing it I'm just writing the text.

    Yes - it is going outside underground it is for a pond filter/pump going into switchbox.

    Part P: Yes, they will be notifying the relevant people before any works are done.

    The person doing the electrics are very competent, but has not worked with the SWA cable for along time and would rather check things are correct before going ahead with anything.
     
  5. Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    13,686
    Thanks Received:
    1,217
    Location:
    Oxfordshire
    Country:
    United Kingdom
    And so competent that they do not know about harmonized cable colours ? :rolleyes:

    TTC
     
  6. sm1thson

    Joined:
    5 Sep 2005
    Messages:
    829
    Thanks Received:
    0
    Location:
    Hull
    Country:
    United Kingdom
    quite rightly so as you dont put plugs on fixed installations!!!
     
  7. Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,379
    Thanks Received:
    424
    Location:
    Cumbria
    Country:
    United Kingdom
    It is sounding similar to one of those armadillo kits.
    The colour scheme which has been adopted by most is:
    Brown - Phase
    Black with green+yellow sleeve - Earth
    Grey with blue sleeve - Neutral.
    As you say, the armour of the cable must also be connected to earth.
     