The dreaded Brittany Combi.............help needed

Also, just going back, can I not use the system gauge when putting air in?

Or must it be done with a seperate gauge?
 
Sponsored Links
Now Im really confused.

Ive totally drained the system and let all the air out of the expansion vessel using the valve.........and its still tell me theres 1 bar of pressure on the gauge.

Sound like the gauge is knakkered.....................
 
It does sound faulty, or a connection to it has a blockage - but it measures the water pressure in the heating system - nothing more & nothing less. As far as your concerned it has no connection to the air pressure in the Expansion Vessel. That must be measured seperately, using the guage on your foot-pump - to approx 0.9bar.

Mr. W.
 