thermocompact vaillant is always over pressured

Joined
23 Dec 2011
Messages
2
Reaction score
0
Location
Warwickshire
Country
United Kingdom
Hi

can anyone help? Our thermocompact vaillant boiler is showing pressure on the guage of between 2 and 3 bars. This has been happening for about three weeks. The reading on the guage goes down to less than 1 if we don't run the boiler for a day or two. Unfortunately it does not seem able to stay between 1 and 1.5 as per the user manual.

How do we get it to stabilise?

Mike
 
Sponsored Links
Hi sounds like your expansion vessel needs pumping up search on here for expansion vessel you should find all the info you need hope this helps Paul.
 
Look at the FAQ on this site and try to repressurise.

But you must do it exactly as stated ( apart from the 10 litre bit ).

Tony
 
Sponsored Links
Thank you both,

Have had a look at the various streams and will act on the advice there.

Will let you know how it goes

Mike
 