TNS earthing

Joined
14 Nov 2005
Messages
378
Reaction score
11
Country
United Kingdom
Does anyone have a picture of what the connection of the sheath to earth cable should look like. I've seen the soldered ones but coming across a lot of BS951 clamps. Been telling the customer to contact the DNO to get sorted is what I have been doing but would like to see how it should be done. Don't have time to return to see. Can't find anything on the net.
TIA. Jack
 
Sponsored Links
Does anyone have a picture of what the connection of the sheath to earth cable should look like. I've seen the soldered ones but coming across a lot of BS951 clamps. Been telling the customer to contact the DNO to get sorted is what I have been doing but would like to see how it should be done. Don't have time to return to see. Can't find anything on the net.
TIA. Jack

Can't find an appropriate picture, but usual way is a BS951 earth clamp fitted to the metal sheath of the supply cable.
 
Sponsored Links
Hello JackC.
Not the best of examples, with the 'snapped tag' etc, but is an 'example' of another TN-S type supply.
tns.jpg


Ed.
 