Initial problem, Trianco Eurostar Boiler failed in Lockout, would reset but then trip again first after 2 or 3 hrs then minutes then not at all. Replaced Photo cell, no joy, replaced Control box, it ran but would cut out after 2-3 hrs again. Now discovered transformer case distorted, replaced transformer, lasted 2 days cutting out 2-3 hrs again. now 2nd transformer burnt out/melted, ideas ?
 
Sponsored Links
type of flue......?

err and have you combustion checked it? etc
 
From previous experience; May I ask if you are a 'Qualified / OFTEC registered technician.'

If you are then get back to me with your ID number and I will explain the problem : :)

If your not a 'Qualified and competent' person, then WHY :eek: Are you working with some thing you know nothing about!
 
Sponsored Links
balanced flue.

try running it with the air hose off.

sometimes exhaust gas gets back into inlet , puts flame out...restarts....puts flame out ...re-starts ,puts flame out...restarts....puts flame out ...re-starts ,puts flame out...restarts....puts flame out ...re-starts
you get the pix. burns out tranformer.

maybe....
 