Trying to spur from a spur

Sponsored Links
sorry guys, new to the forum stuff, didnt realise writing with caps lock on was such a big deal.

SORRY
 
The basic concern is that it should not be possible to overload any given cable run, even if someone (for example) cobbles a 3kW heater onto your spur. Provided the fuse or breaker will disconnect in such a case before the cable is seriously overloaded, in principle it's OK.

As always you need to think not only about what you are installing now- even though it only draws 40W- but what some idiot might add to it later.
 
Sponsored Links
Exactly the same argument about future idiots can be made no matter how many FCUs he uses - he could install dozens, one for each lamp, and your concern would be just as valid, or invalid, if he installed none.

Existing setup:

[SOCKET]---------[FCU w.3A fuse]---------[140W load]

Proposed:

[SOCKET]---------[FCU w.3A fuse]---------[140W load]
. . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .|
. . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .|--------[40W load]

Nothing wrong with that at all.
 