I'm having a 'below sink' unvented water heater installed in the loft. It needs a pressure relief valve installed in the pipework along with it. Has the drain coming from the PRV & tundish got to be copper? or can it be PE-X barrier pipe?
4xpaws said:I'm having a 'below sink' unvented water heater installed in the loft. It needs a pressure relief valve installed in the pipework along with it. Has the drain coming from the PRV & tundish got to be copper? or can it be PE-X barrier pipe?
4xpaws said:Thanks for comment.
One reason amongst others is too long a pipe run is needed to fit thermal store. 30m+ run needed. Its for 3rd floor and storage cylinder's in basement.
4xpaws said:Secondary return -what's all that about? Returning to where?
Fraid not, they come with a PRV and you have to allow 4 meters of supply 15mm pipe for expansion back up the supply pipe before a draw off on said supply.........or 2 metres of 22mm pipe I would run copper and use a 22x35 reducer as a tundish.......in fact I`ve done 2 now ,as they are not covered by unvented certificating which I aint gotjay1 said:does it need to have prv and tundish if it is storing less than 15 litres, im pretty sure its doesnt need to.
A DHW secondary circulation pump can be fitted to a thermal store heat bank.
You haven't answered the main quetion of what it's for.
with a PRV and you have to allow 4 meters of supply 15mm pipe for expansion back up the supply pipe before a draw off on said supply.........or 2 metres of 22mm pipe
You want to use a 10 litre unvented heater to run a bathroom?