Mogget. You are confused ... If you do not understand the system please leave it for expert to answer.
Mogget. You are confused ... If you do not understand the system please leave it for expert to answer.
I suggest you heed your own advice. Over and out.
All I can see is:
1 No Pump
1 No 2 Port motorised Valve
1 Remote thermostatic cylinder sensor coupled to a diverting (3 way) thermostatic valve http://www.draytoncontrols.co.uk/TapstatCylinderControlsDatasheet.aspx
2 No Microbore manifolds
1 No 15mm Gate valve (A bypass maybe?)
Lots of confusing bubble wrap
So my impression is the system is fully pumped but the hot water has only a thermostatic control on it
I am unable to see feed or vent pipes to the system in those photo's
An S plan conversion looks on the cards by replacing the cylinder controls with a 22mm motorised valve and electric cylinder stat.
Replace existing 15mm cylinder primaries with 22mm
A suitable S plan programmer
A room thermostat if not already fitted.
A visit by a qualified electrician to replace scorched cables install a wiring centre with new cables (heat resisting where appropriate) and clip in place any cables found fit to remain.
The installation is generally untidy and to be honest I would recommend a heating engineer check it over to see what else comes to light.