My boiler has started to misbehave! The hot water runs ok for a few minutes then turns cold. Looking at the read out on the boiler the water temp is shooting up (70 degrees!), then I guess the safety systems are cutting in . Runs ok, it seems, for the radiators. Do I have a dead boiler or is it fixable?
 
Sponsored Links
Water flowrate from hot tap in liters per minute would help.
 
Sounds like a blocked secondary heat exchanger.

Totally fixable !

Tony
 
Thanks for your answers

I estimate flow rate to be about 8 litres per minute.

If it's fixable - what sort of price to sort it out?
 
Sponsored Links
No estimates- what is it? Measure it.

For a blocked HWHE, temperaure would not be 70
 
Thanks

Have let hot tap run into container for 1 min - then measured. Result 8.5 litres per minute.
 