Yes valves open. My power flusher can push water through the boiler from flow to return or return to flow as if it was an open 15 mm pipe, hardly any pressure difference between the two implying no flow restriction, blockage or similar flow inhibited. When I shorted flow to return it was a 22 mm flex pipe 300 mm in length and about 400 mm down from the boiler below the magnetic sludge trap and feed in Tee. So about 1.2 metres of pipe from flow to return take offs on the boiler underside.
The power flusher blasted out any air traps, the AAV is definitely clearing the pump rotor chamber. The only thing I have not yet tested is the bypass valve and taken the pump out to look at the rotor itself (I have experienced one pump which, when I removed it, had no blades on the rotor, it was just a circular hub on the shaft. Goodness knows how they disappeared, grit?).
so with little or no restriction the next place to look will be hoses and pump but I didn’t want to break in there until I’d got an o ring set.