What size should the Tails be to a domestic fuse board?
Yes that what I thought just having a conversation with a mate and the earth to PME the system 16mm ? Obviously from the CU to N in cut out ?
Yes that what I thought just having a conversation with a mate and the earth to PME the system 16mm ? Obviously from the CU to N in cut out ?
Always know what the DNO is doing, a 16mm copper (25mm Aluminium) (Imperial .0225 in) service cable is rated to carry over 100A in our tables and may well be fused accordingly.
If ever (we) I change or move a CU we always put in 25mm tails and a 16mm main bond as a matter of course. Just think it future proofs it to a certain extent.
IF - meanwhile...If the cut out and meter ever gets changed, the DNO never replace your tails, and since their equipment will often be sealed it's difficult for you to change them.
At least in the context of this thread (meter tails) I think one of the problems is that BS7671 itself does not give CCCs for non-touching singles for CSA's <25mm², which one imagines will be a little higher than for touching singles or muticore cables. For 16mm² 'clipped direct' touching singles it gives 87A (the 'in free air' {touching and non-touching} columns are blank for <25mm²!). For 2-core 16mm², it gives 94A for 'in free air'. One therefore imagines that the corresponding rating for 16mm non-touching singles in free air, if they gave it, probably would, indeed, be of the order of 100A, if not more - so perhaps no real inconsistency there.Always know what the DNO is doing, a 16mm copper (25mm Aluminium) (Imperial .0225 in) service cable is rated to carry over 100A in our tables and may well be fused accordingly.
One therefore imagines that the corresponding rating for 16mm non-touching singles in free air, if they gave it, probably would, indeed, be of the order of 100A, if not more
Indeed. I hope you're making a good recovery.I suspect that is the case, and as the tails between the cut-out & the meter are "ours" they will be asigned our rating which will probably be higher than BS 7671. (I can check as I am off work following an operation)One therefore imagines that the corresponding rating for 16mm non-touching singles in free air, if they gave it, probably would, indeed, be of the order of 100A, if not more
As we've discussed many times before, I think one of the issues is that virtually all these tables of 'ratings' tend to be very conservative - so the variation we see is probably nothing more than varying degrees of conservatism.Amazing how a meter can change a cable rating depending upon which side it is on! Somewhere around my desk is an old BICC ratings book It would be interesting to see what ratings that assignes