Morning all,
What would you do, decisions decisions.
Customer wants power out to a summer house.
He has purchased most of the materials already (2core swa 10mm sockets and conduit) and wants a CU supplied & installed in the outbuilding for lights + sso's.
Now the house is TT converted to PME (no pme label) no spareways on cu & he doesn't want the cu changed (place is minging so I'm chuffed with that) & the outbuilding is 12mtrs away.
I was planning on using henlys to split the 25mm tails, in to a hager switch fuse, run 10mm swa from switchfuse to outbuilding into 2 way cu with 30mA rcd as main switch & TT the outbuilding.
Now I'm doubting myself & thinking maybe RCD at the switch fuse ?
Or
Bin his 2 core put in 3 core and export the pme.
What would you do, decisions decisions.
Customer wants power out to a summer house.
He has purchased most of the materials already (2core swa 10mm sockets and conduit) and wants a CU supplied & installed in the outbuilding for lights + sso's.
Now the house is TT converted to PME (no pme label) no spareways on cu & he doesn't want the cu changed (place is minging so I'm chuffed with that) & the outbuilding is 12mtrs away.
I was planning on using henlys to split the 25mm tails, in to a hager switch fuse, run 10mm swa from switchfuse to outbuilding into 2 way cu with 30mA rcd as main switch & TT the outbuilding.
Now I'm doubting myself & thinking maybe RCD at the switch fuse ?
Or
Bin his 2 core put in 3 core and export the pme.