Hi, I was hoping that someone could confirm or correct what i intend to do do with suppling a summer house with power.
From the Main C/U in the house i will take 4.0mm2 SWA off a 32A CB up into the roof and along to the corner of the house. Now this is what i am unsure of - There a fixed awning between the house and summer house, i would like to run the the SWA along underneath, clipped to the awning and into the summerhouse. I will then take the SWA into a MK IP65 Garage C/Unit 40A 30mA RCD+1x6A 1x16A SP CB. From that i will have a switch to strip light on the 6A CB & a ring main with 4 double sockets and a spur to a outdoor socket on the 16A CB.
I am fully aware of part P compliance and that it is notifiable work.
I have attached a pic of the proposed
Thank you
From the Main C/U in the house i will take 4.0mm2 SWA off a 32A CB up into the roof and along to the corner of the house. Now this is what i am unsure of - There a fixed awning between the house and summer house, i would like to run the the SWA along underneath, clipped to the awning and into the summerhouse. I will then take the SWA into a MK IP65 Garage C/Unit 40A 30mA RCD+1x6A 1x16A SP CB. From that i will have a switch to strip light on the 6A CB & a ring main with 4 double sockets and a spur to a outdoor socket on the 16A CB.
I am fully aware of part P compliance and that it is notifiable work.