Over the last month I've noticed that the bath tap in the upstairs bathroom will go stone cold every couple of minutes for about 30 seconds. The only way to get hot back out is to turn the cold off and the hot to maximum and then after about 30 seconds it goes back hot again. It doesn't seem to do this out of the downstairs taps.

The boiler is downstairs and about 8 years old.
 
Sponsored Links
Do you know the age of the property? Could be a failing thermostatic mixer, could be a mixer tap crossing over.
 
  • Thanks
Reactions: m0t
Do you know the age of the property? Could be a failing thermostatic mixer, could be a mixer tap crossing over.
House is 1920's, the downstairs pipework is about 15 years old and the upstairs is 2 years old. No mixers anywhere on the pipework except the showers. Bath tap is two lever style taps (one hot and one cold).
 
  • Thanks
Reactions: CBW
Could be the shower passing. Are you able to isolate the cold to the boiler and run the bath tap?
 
  • Thanks
Reactions: m0t
Sponsored Links
No - the hot and cold feeds to the downstairs shower are tee'd off the run to the upstairs bathroom. Sounds like it could be a strong possibility given where it is in the pipework

It's an old mira thermostatic shower although I did change the thermostatic cartridge on it a few years ago.

Is there any way to check the shower itself?

Edit: not sure if it makes a difference but the downstairs shower was the main shower until about a year ago but probably hasn't been used by anyone in about a year. Would being unused for so long cause an issue?
 
Are you able to isolate the cold to the boiler and run the bath tap?
So the boiler (assumed combi) will have an isolation valve for the cold inlet feeding the hot supplies, if you turn this off and run the hot tap for the bath it should stop.
 
  • Thanks
Reactions: m0t
Sorry, completely misunderstood.

I've just done that and didn't get any water come through
 
  • Thanks
Reactions: CBW
To update we had the plate heat exchanger replaced yesterday and now the problem appears to be fixed.

Managed to run two baths without the tap going cold. Not sure if that means it's only a matter of time for the main heat exchanger to go or not?
 
  • Thanks
Reactions: CBW

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top