worcester bosch 35cdi 11 rsf

Joined
29 Nov 2006
Messages
2
Reaction score
0
Location
Yorkshire
Country
United Kingdom
when ch is on noticed prv was releasing water. pressure was high. i fit a new expansion vessel with various charges but no different. ch/hw work ok. when i release the pressure of ch back to 1 bar, put ch on, over a few hours it creeps up. over night the heating was off and pressure went up at least 0.5 bar. i now have noticed that when hw tap is turned on the guage flickers and goes up 0.2 bar, tap off back down.[filling key is out] i think it must be passing water from hw side [mains water]. boiler is about 3 years old.can anyone advise thank you regards tonyk
 
Sponsored Links
hw heat exchanger at the back on the left hand side next to the expansion vessel.
 
ollski said:
hw heat exchanger at the back on the left hand side next to the expansion vessel.
d0 you mean the water to water heat exchanger as per parts book. this on my 35cdi is located at the front middle
 