My Father in law has a fault with his Greenstar Condensing HE Combi.
The pilot light cuts out after 15 seconds. The Heat exchanger can be heard filling with water , but trickeling as though its not under pressure. The pressure Gauge shows in the green at 3 Bar. The display reed Fault code E4.
Any comments would be Welcome. Thanking you in advance
 
Sponsored Links
Sponsored Links
It is more likely to be a blocked condensate pipe as you would not hear the system water in the aweful situation of having air with it.

The pressure at 3 Bar is double the normal pressure. Let some out from a rad bleed point.

Who over pressurised the boiler?