central heating only comes on with h water, stumped engineer

Goto page Previous  1, 2, 3 ... 21, 22, 23, 24, 25  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Mikefromlondon

from United Kingdom

Joined: 06 Aug 2011
Posts: 1600
Location: London,
United Kingdom
Thanked: 28 times

PostPosted: Fri Mar 16, 2012 8:14 pm Reply with quote

Thanks Matt, I can see the point now, since if the pump was connected to the return tapping , it would force the water in correctly through the boiler's heat exchanger. All depending of course how the pump is connected and in which direction it is flowing, but yes, good point and thanks again. cheers.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Fri Mar 16, 2012 8:37 pm Reply with quote

Mikefromlondon wrote:

If as Doitall is asking Bill whether he traced the pipes with the pump running or without the pump running, I am of the opinion, that he should check with the pump running since that is how the water will be forced to flow, whereas, just relying on gravity it may run or flow in the opposite direction and give us confused results, so I really don't know what would be expected if the pump was not running, but its just my opinion, not an attack on anyone's suggestion otherwise. you guys are more expert but it would be nice to know the resaon why the pipes should be checked without the pump running.


What I asked for is not an option, I/we need to know, and until we get answer we are wasting out time.

For your information only the pump is sucking the water from the boiler, port AB will get hot first with the pump running, even when it's connected wrong.
Back to top
The following user says thank you to doitall for this useful post:
bonkersbill (17 Mar 2012)
 Alert Moderators
UpgradeME

from United Kingdom

Joined: 06 Feb 2011
Posts: 221
Location: United Kingdom
Thanked: 24 times

PostPosted: Fri Mar 16, 2012 8:53 pm Reply with quote

Baxi Installation Manual wrote:

5.6 Water Connections
1. The boiler has one return and two flow tappings. Rc1 (1in
BSP). The flows are the two upper tappings. The return is
the lower position tapping and is marked RETURN. It is
essential the flow and return pipes are connected to the
correct tappings.
Back to top
 Alert Moderators
bonkersbill

from United Kingdom

Joined: 28 May 2010
Posts: 110
Location: United Kingdom

PostPosted: Sat Mar 17, 2012 9:29 am Reply with quote

pipes to boiler
pipes to boiler
boiler conection
boiler conection

Thanks Doitall, at last an explanation i understand as to why testing with the pump on does not work, this could have saved me alot of time had i understood this earlier.
Heres my solution to figure out which 28mm pipe is which, i will close off all rads, water tanks and valves, drain the system from a downstairs rad that has a drain plug lower than the boiler, remove the cylinder pipe at 3pv port B because its easy to get to, remove the top 28mm pipe conected to the boiler, i will then either blow, shout or pour water down this pipe with my missis on the other end, if any of these comes out of the 28mm pipe, its connected wrongly, if they come out of the boiler then its piped correctly, can anyone see any flaws or reasons not to do this?
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Sat Mar 17, 2012 9:43 am Reply with quote

icon_rolleyes.gif The sooner you, stop thinking and leaving it to the pros the better your chances are icon_rolleyes.gif

Your plan is flawed because we don't know what else is connected wrong.

Put the two pics together in a drawing, and ID the capped pipe
Back to top
 Alert Moderators
bonkersbill

from United Kingdom

Joined: 28 May 2010
Posts: 110
Location: United Kingdom

PostPosted: Sat Mar 17, 2012 11:30 am Reply with quote

i've already put the 2 pics on my last drawing showing the capped off pipe. At the moment i have the gas fire out, if im going to do any tests i need to do them now because i need to put it back for my heating and hot water.
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Sat Mar 17, 2012 12:02 pm Reply with quote

If your last drawing was accurate the system would work.

You need to do the tests we asked for, with the pump off electrically.

or trace the pipes.

Test with the MV in all 3 positions, and the boiler on low.
Back to top
 Alert Moderators
bonkersbill

from United Kingdom

Joined: 28 May 2010
Posts: 110
Location: United Kingdom

PostPosted: Sat Mar 17, 2012 12:21 pm Reply with quote

ive done all the tests with the pump off and ive traced the pipes to the best that can be done by eye other than under the boiler, i have had 2 carpets up and been through 2 access holes to be blocked off by brick walls. if ive missed some new tests somewhere then what are they?
Back to top
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Sat Mar 17, 2012 12:31 pm Reply with quote

doitall wrote:
If your last drawing was accurate the system would work.

You need to do the tests we asked for, with the pump off electrically.

or trace the pipes.

Test with the MV in all 3 positions, and the boiler on low.


Looking through He has already done this
bonkersbill on march 1st wrote:
well lets see how this changes things, only managed 2 test today,
pump disabled, prog set HW only, 3pv mid gets pipe to pump hot 1st,
pump disabled, prog set HW only, 3pv HW gets pipe to bottom of tank hot 1st


But then again that seems to contradict this
bonkersbill also on march 1st wrote:

Test i did was remove red wire from pump, set 3pv to HW and boiler to low with prog to HW on, the pipe to the bottom of the tank was red hot and the pipe to the 3pv AB was warm to hot, sorry i missed which got hot 1st but it was unmistakable that the one to tank was hottest.
Back to top
 Alert Moderators
bonkersbill

from United Kingdom

Joined: 28 May 2010
Posts: 110
Location: United Kingdom

PostPosted: Sat Mar 17, 2012 12:38 pm Reply with quote

Yes i believe i pointed this out that i had both pipes get hot in different tests. this is why i proposed disconecting the pipes to find out which was which.
i was told after these tests i needed to find out what was happening at the boiler, this i have now done, so what now?
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18839
Location: Bath,
United Kingdom
Thanked: 1515 times

PostPosted: Sat Mar 17, 2012 12:53 pm Reply with quote

Mark the pipes where they are outside of the boiler going up the wall, so you know exactly which is the flow and return.

There is also an issue with the heating return getting hot from memory.

You can disable the pump from the wiring center if it's difficult to get at the pump.

Then do the tests again and post the 3 results.

HWS only, which pipe gets hot.

Mid position which pipe gets hot.

Heating only which pipe gets hot.
Back to top
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Sat Mar 17, 2012 12:56 pm Reply with quote

Bill the two tests quoted should yield the same results
Quote:

Test i did was remove red wire from pump, set 3pv to HW and boiler to low with prog to HW on, the pipe to the bottom of the tank was red hot and the pipe to the 3pv AB was warm to hot


Quote:
pump disabled, prog set HW only, 3pv HW gets pipe to bottom of tank hot 1st


it is hard to make out from the photo, is the 3port B connection going to the bottom or top cylinder connection?

Matt
Back to top
 Alert Moderators
bonkersbill

from United Kingdom

Joined: 28 May 2010
Posts: 110
Location: United Kingdom

PostPosted: Sat Mar 17, 2012 1:49 pm Reply with quote

Port B goes to the top pipe in cyl.
The return pipe we thought was getting hot was the 15mm which teed off to 22mm towards the boiler, this is capped off. i can only make a reasonable guess as to which of the 28mm pipes is which when it goes through 8 inch of chimney, even so, from this point up to the pump/cyl i cant tell which is which, hence my suggested test or any other, the heat test with pump disconnected definatly showed both pipes getting hot in different tests. My suggestion of disconecting the port B and top of the boiler to find out if these are both the same pipe could resolve this baring any hidden tees which we cant varify anyway.
Back to top
 Alert Moderators
stardanny

from United Kingdom

Joined: 14 Nov 2007
Posts: 1154
Location: Buckinghamshire,
United Kingdom
Thanked: 165 times

PostPosted: Sat Mar 17, 2012 2:12 pm Reply with quote

bonkersbill wrote:
pipes to boiler
pipes to boiler
boiler conection
boiler conection


The pipe at top is 28mm flow.
The pipe at the back top is the 22mm flow that is capped when it changed to fully pumped.
The bottom one is the injector tee with 28mm return at bottom of tee and 22mm heating return at side of tee.

There could be trace of where the old heating pump used to be with a piece of pipe in place of pump. Could be in box in or under ground floor.

This is fine. Correctly piped.

The best way is to trace / look both 28mm pipes from boiler tappings to cylinder tapping/pump inlet. Take your time and work out. Any good pipe fitter like me can work out which it which.

Dan.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52905
Location: London,
United Kingdom
Thanked: 3331 times

PostPosted: Sat Mar 17, 2012 2:14 pm Reply with quote

bonkersbill wrote:


i will then pour water down this pipe with my missis on the other end, if any of these comes out of the 28mm pipe, its connected wrongly, if they come out of the boiler then its piped correctly, can anyone see any flaws or reasons not to do this?



I like that idea !

Make sure she wears a thin white tee shirt so that you can easily see if she has got wet.
Back to top
The following 2 users say thank you to Agile for this useful post:
stardanny (17 Mar 2012), gaswizzard (17 Mar 2012)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page Previous  1, 2, 3 ... 21, 22, 23, 24, 25  Next
Page 22 of 25

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
28cdi worcester bosch boiler - engineer stumped! 12 260 Sat Sep 10, 2011 10:40 am
Our Central Heating has our plumber stumped...NEED your help 20 800 Wed Dec 21, 2011 7:43 pm
Heating has me stumped 10 540 Wed Sep 27, 2006 4:13 pm
HELP- 3 heating engineers stumped!! 27 1480 Tue Dec 26, 2006 10:57 pm
Stumped: hot water from cold tap for 10 seconds only 3 120 Wed Aug 27, 2014 8:40 pm


 