BrokenBoiler1976

from United Kingdom

Joined: 31 Dec 2012
Posts: 2
Location: Gloucestershire,
United Kingdom

PostPosted: Mon Dec 31, 2012 3:59 pm Reply with quote

Hi all,

I ran out of oil and the boiler locked out.

Since then I have bled the oil pump and now it no longer fizzes oil and air but just runs oil so I assume all is ok there. I have also unscrewed the bolt (point 2 in the image) and oil squirts from there when I click the unlock button so I also assume that oil is making it into the burner.

I have also checked the photo cell (4 in the image) and that is perfectly clean.

The odd (seems it to me anyway) thing is that when it tries to fire up I can see a bright spark at point 1 in the image (as a black tube enters the silver block) and smoke is emitted (not much and it smells electric rather than oil based). The boiler tries to fire up but a few seconds after I hear a click noise (the ignition?) it locks out again.

I am at a loss at to why the boiler isn't firing up - the motor whirs like it used to but the 'whoosh' of the oil firing up no longer occurs.

Any ideas? Any help appreciated!!!

PS - in the second image below you can see that the copper pipe leading into my oil tank is a bit loose - in so much as it can be lifted up a few inches - is that an issue???

Thanks,
Matt.


Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3341
Location: Humberside,
United Kingdom
Thanked: 504 times

PostPosted: Mon Dec 31, 2012 7:57 pm Reply with quote

Sounds like there is no oil coming through the nozzle.
The flame you see is the spark ignition trying to light the non existent
oil.
Back to top
 Alert Moderators
Mike2007

from United Kingdom

Joined: 10 Feb 2007
Posts: 1072
Location: Cumbria,
United Kingdom
Thanked: 17 times

PostPosted: Tue Jan 01, 2013 6:47 pm Reply with quote

when it goes through the "motions" of starting, use a small screwdriver over the top of the solenoid (top of pump) to detect if there is a magnetic field inside the solenoid?
If there isn't, the solenoid isn't opening to let pressurised oil out to spray.
Your pump may also have seized due to lack of oil inside the pump. You will need to remove pump completely and see if the shaft that turns the pump still rotated?? If its stiff its knackered, new pump.

Back to top
 Alert Moderators
Boilerman2

from United Kingdom

Joined: 10 Jun 2009
Posts: 4929
Location: Suffolk,
United Kingdom
Thanked: 920 times

PostPosted: Tue Jan 01, 2013 8:09 pm Reply with quote

BrokenBoiler1976 wrote:

The odd (seems it to me anyway) thing is that when it tries to fire up I can see a bright spark at point 1 in the image (as a black tube enters the silver block) and smoke is emitted (not much and it smells electric rather than oil based)




And that my friend is your problem one of the HT ignition leads has burnt out causing a short to earth this is why you can see a bright spark in the wrong place and a smell of electrical burning - oh and just to add to your woes - every time you try to start the burner you are injecting a quantitiy of oil into the combustion chamber - so if you have tried more than 6 times things could be very interesting when you get it to fire up!!

Thats why you should not reset from Lockout more than twice without rectifying the fault!! errr Good luck! icon_wink.gif
Back to top
 Alert Moderators
BrokenBoiler1976

from United Kingdom

Joined: 31 Dec 2012
Posts: 2
Location: Gloucestershire,
United Kingdom

PostPosted: Tue Jan 01, 2013 8:24 pm Reply with quote

Boilerman2 wrote:
BrokenBoiler1976 wrote:

The odd (seems it to me anyway) thing is that when it tries to fire up I can see a bright spark at point 1 in the image (as a black tube enters the silver block) and smoke is emitted (not much and it smells electric rather than oil based)




And that my friend is your problem one of the HT ignition leads has burnt out causing a short to earth this is why you can see a bright spark in the wrong place and a smell of electrical burning - oh and just to add to your woes - every time you try to start the burner you are injecting a quantitiy of oil into the combustion chamber - so if you have tried more than 6 times things could be very interesting when you get it to fire up!!

Thats why you should not reset from Lockout more than twice without rectifying the fault!! errr Good luck! icon_wink.gif


Thank you all for your replies. I will call an engineer and tell him what you have said so he's pre-warned! An expensive start to the new year icon_wink.gif

Thanks again - very helpful of you all and have a HAPPY NEW YEAR!
Back to top
 Alert Moderators
Mike2007

from United Kingdom

Joined: 10 Feb 2007
Posts: 1072
Location: Cumbria,
United Kingdom
Thanked: 17 times

PostPosted: Tue Jan 01, 2013 9:13 pm Reply with quote

Boilerman2 wrote:
BrokenBoiler1976 wrote:

The odd (seems it to me anyway) thing is that when it tries to fire up I can see a bright spark at point 1 in the image (as a black tube enters the silver block) and smoke is emitted (not much and it smells electric rather than oil based)




And that my friend is your problem one of the HT ignition leads has burnt out causing a short to earth this is why you can see a bright spark in the wrong place and a smell of electrical burning - oh and just to add to your woes - every time you try to start the burner you are injecting a quantitiy of oil into the combustion chamber - so if you have tried more than 6 times things could be very interesting when you get it to fire up!!

Thats why you should not reset from Lockout more than twice without rectifying the fault!! errr Good luck! icon_wink.gif


Yeah missed that point! icon_confused.gif There is occasions where someone has refitted the burner casings badly only to nip the HT leads and power to electrodes arc out! New Heatslave HT leads about a tenner!
Good luck with the fix.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Worcester heatslave 25/32 Hot lockout 20 240 Sun Nov 10, 2013 10:10 am
Intermittent lockout on worcester heatslave 15/19 6 760 Wed Dec 26, 2007 7:39 pm
Worcester Bosch Heatslave 15/19 lockout and not firing 5 80 Mon Nov 18, 2013 6:18 pm
Worcester Oil Heatslave 20/25 lockout problem HELP 3 1000 Thu Oct 23, 2008 9:10 am
Worcester oil Heatslave 15/16 - LockOut reset location? 4 1080 Thu Mar 16, 2006 7:34 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.