PostPosted: Mon Oct 26, 2009 4:44 pm    Post Subject:
Reply with quote Thanks

denvillesman wrote:
the model numbers are V4043H1106 for the airing cupboard one and 272848 for the ones in the loft.

OK, they are normally closed zone valves with an auxiliary switch. When you apply voltage to the brown and blue wires the valve opens and the auxiliary switch closes, connecting the grey and orange wires. The grey is usually connected to a permanent 240 supply; the orange goes to the boiler switched live terminal.

Edit: Some version of this valve have a white wire as well. This is not used in your set-up.

However we still have the strange problem with your voltages on the thermostat. I haven't worked out what is happening yet; will get back to you.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3177
Location: Sussex,
United Kingdom
Thanked: 72 times

PostPosted: Mon Oct 26, 2009 5:29 pm    Post Subject:
Reply with quote Thanks

I think I am there.

Quote:
I say anything else I want to say what the connections are in this newly found junction box (JB), as there seems to me to be something wrong
Stat R - ZV grey
Stat Y - ZV brown
Stat B - not connected to anything at all

That means Stat R is the supply from the programmer CH ON terminal and Stat Y is the switched supply to the valve. Unusual, but OK. The normal method is to connect the grey wire to a permanent supply terminal in the junction box.

Do you mean the stat B is not connected at the junction box?
If so we can make use of it.

Disconnect the Satchewell stat

Connect stat R wire to receiver L
Connect stat Y wire to receiver B
Connect stat B to receiver N
Link receiver L and A

At the junction box, connect the disconnected stat B wire to a neutral point, e.g same as blue from the zone valves.
Back to top
The following user says thank you to D_Hailsham for this useful post:
denvillesman (27 Oct)
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 255
Location: Tyne and Wear,
United Kingdom
Thanked: 10 times

PostPosted: Mon Oct 26, 2009 8:28 pm    Post Subject:
Reply with quote Thanks

D_Hailsham wrote:
I think I am there.

Quote:
I say anything else I want to say what the connections are in this newly found junction box (JB), as there seems to me to be something wrong
Stat R - ZV grey
Stat Y - ZV brown
Stat B - not connected to anything at all

That means Stat R is the supply from the programmer CH ON terminal and Stat Y is the switched supply to the valve. Unusual, but OK. The normal method is to connect the grey wire to a permanent supply terminal in the junction box.

Do you mean the stat B is not connected at the junction box?
If so we can make use of it.

Disconnect the Satchewell stat

Connect stat R wire to receiver L
Connect stat Y wire to receiver B
Connect stat B to receiver N
Link receiver L and A

At the junction box, connect the disconnected stat B wire to a neutral point, e.g same as blue from the zone valves.


I think you are there too mr hailsham just worked it out this way too but never noticed the second page so you beat me!
but i will concur

In case you are wondering denvillesman the strange voltage readings are due to the coil of the motor in the zone valve being connected to neutral (which is why the yellow seemed like a neutral)

matt
Back to top
 Alert Moderators
denvillesman

from United Kingdom

Joined: 16 Oct 2009
Posts: 9
Location: Hampshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 27, 2009 12:21 pm    Post Subject:
Reply with quote Thanks

icon_biggrin.gif icon_lol.gif icon_biggrin.gif icon_lol.gif icon_biggrin.gif
Well, D Hailsham (I guess Derek or Dave?), it took a little while, but as I have said already I admire your patience, particularly with the innocents such as myself. YES it is all working fine with the final wiring instructions.

I suppose with the glory of hindsight it was quite straightforward in the end when we had established the wiring went to a ZV. But I daren't think I could have done it without you. Thank you so much.

And nice to see that A N Other in the form of Matt1e was clearly keeping an eye on the string, thanks for the final observation on the voltages.

Bizarrly now, because of the mild weather I shall have to wait a while before having the fun of playing with the toy from the comfort of my sofa.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Honeywell CMT921 24 hour wireless Programmable Thermostat 9 380 Thu Oct 15, 2009 9:34 pm
Ancient Honeywell Room Stat 3 180 Wed Jan 07, 2009 4:39 pm
Honeywell T6160B to CM907 Room Stat, Some Problems? Updated 14 1020 Thu Oct 16, 2008 11:37 am
New Room Stat Honeywell Digital DT200 2 380 Sat Oct 04, 2008 9:06 pm
Wiring a Honeywell CM67RF room stat 4 1780 Sun Nov 06, 2005 4:16 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.