What ever you run is going to have to be contained in earthed metal to keep if free from 30mA RCDs, and allow proper division of the installation at the CU, and as you have a TT incommer, you're going to have to install a 100mA time delayed RCD at the mains along with some sort of OCPD.
Can you not use SWA if you drill through the wall at a steep angle, so the bend in the SWA is much reduced?
For something like this, I would run a SWA and gland it off into a conduit end box with some extention rings fitted, and screw the CU to that so the cores remain fully contained.
If SWA really isn't viable, then maybe you can use ali tube. Remember you only need enough current to flow to operate a 100mA RCD, not full operating current of the OCPD.
Other options are pyro, providing you can still find anywhere that sells it in big enough CSA for this and you are used to working with it, steel conduit all the way between the incommer and the sub mains board, but again this is tough if you're not used to working with it, or maybe you could look at a departure from the regs and use split concentric cable?