Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
mcquitmp

from United Kingdom

Joined: 23 Jul 2007
Posts: 16
Location: Ipswich,
United Kingdom

PostPosted: Thu Sep 13, 2007 6:33 pm Reply with quote

I have a 4 pole 32A Rotary Isolator switch which I am planning to use to Isolate the supply to a Hot Tub. The supply is fed from a 3 Core 6mm2 SWA cable.

The Isolator switch is obviously designed to switch 3 phase and Neutral and has two other earth connection points.

My question are -

Why is the Neutral connection point smaller than the other 3 connection points (It does not indicate neutral on it but it seems a safe bet) - allowing only a smaller cable to be connected to it?

Can I use one of the phase connection points to switch the neutral instead since I am only single phase anyway?

I assume I connect the 3rd core (used as Earth) along with the Armour to the earth connection points and this remains unswitched?

The switch is CED Rotary switch supplied by Screwfix.

Advice appreciated.

After I have finished the complete installation will be inspected, tested and certificated by a Part P qualified electrician - but I'm trying to get it right from the start and don't want to look a complete idiot.

Thanks...
Maurice
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36113
Location: Hampshire,
United Kingdom
Thanked: 1272 times

PostPosted: Thu Sep 13, 2007 6:50 pm Reply with quote

In 3-phase supplies the Neutral carries either no load, or a reduced load.

If you are switching a single-phase circuit use two of the Phase contacts.

The earth must be unswitched.

the armour must be earthed at least at the supply end.

If you are in England this is notifiable work and not very suitable for an amateur. the qualified electrician is supposed to install it, and test and certify his own work. Only a local Goverment inspector can inspect and certify someone else's work, and will have to see it during installation as well as at completion. You have to notify before starting work.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
2 way switch wiring with single core cable? 17 3760 Sun Oct 31, 2010 6:24 pm
2-core wiring in switch to 3-core loft 2 fluorescent lights 3 820 Wed Apr 15, 2009 2:18 pm
Wiring a light switch with 3 core wire from a plug 9 240 Fri Apr 27, 2012 5:24 pm
Wiring for light with a 2 gang switch with 3 core cable 8 3580 Wed Nov 03, 2010 8:58 pm
Wiring 3 core light to ring main and extractor fan 3 3160 Sun Oct 05, 2008 5:18 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.