Hi, all. A friend of mine has just had a new boiler and cntral heating system to replace his original one. For some reason, the old immersion heater was connected to 1.5mmT&E. The electrician that came to wire up the new system including the new immersion heater, said that the 1.5mm T&E cable was ok to leave in and wire up to.!. Is this the case or was he just being lazy not wanting to rewire with 2.5mm T&E. The cable is on its own circuit and the length is aprox 25metres. Also, I was wondering if the fuse fitted is ok at 16amps, i'm just a little concerned that the safety device i.e the circuit breaker can stand more than the cable?
Any advice would be appreciated.
Andy Stu
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8439
Location: United Kingdom
Thanked: 197 times

PostPosted: Wed Nov 05, 2008 1:28 am Reply with quote

how is the cable run? In particular does it run through any insulation?
Back to top
 Alert Moderators
Andystu

from United Kingdom

Joined: 17 Feb 2007
Posts: 9
Location: Nottinghamshire,
United Kingdom

PostPosted: Wed Nov 05, 2008 9:24 am Reply with quote

I believe it runs from the consumer unit which is located in the single storey garage, up through the garage lof space which has a small amount of insulation, maybe 50mm then under the floor boards and into the airing cupboard. If the route is vital for the calculation then I can find out exactly in more detail.

Thanks,

Andy Stu
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Wed Nov 05, 2008 9:50 am Reply with quote

The route isn't vital - 1.5mm˛ T&E can safely carry more than 13A even if insulated and in conduit.

A 16A breaker is also fine, but the outlet in the airing cupboard should be fused at 13A.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
immersion heater cable size 7 620 Mon Nov 17, 2008 11:49 am
Making safe live cable end. 6 260 Fri Feb 18, 2011 2:04 pm
Safe termination of cable 4 240 Fri Dec 16, 2011 10:37 pm
cable routing safe zones 4 14140 Sat Feb 10, 2007 6:43 pm
Safe to use cable reel for Xmas lights? 4 240 Tue Nov 30, 2010 9:40 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.