FITTING NEFF OVEN & SMEG HOB
9 Dec 2004
I'm replacing an existing stand alone Electric Cooker (protected by a NSB40 (40A) Wylex Minitaure Circuit Breaker) on a radial spur. I have no idea about the existing rating of the cable in the wall.
I will be fitting a NEFF double oven( 5.1 kw) and a SMEG Hob (6.6 kw)
Can I connect this to the same Cooker outlet junction box?
Is the 40A circuit breaker adequate or will I need to move up to 50A if the following rule holds good...
5100W + 6600W = 11700W/240V = 48.75 A
What size three core cable do I need from the cooker and the hob to the cooker outlet junction box?
Lots of recent cooker posts – do a search.
You have two appliances hob at 6.6 and cooker at 5.1. We have harmonised with Europe and you must use 230v in the calculations.
6.6+5.1 = 11700w
11700w/230v = 50.8A.
Allowing for diversity max demand is 10+(30% * 40.8) = 22.26A
Therefore in theory 4mm should be ok for the appliances. However with a 40A MCB you will need at least 6mm if not 10mm depending on the way your cables are installed.
The two appliances can be on the same circuit since we are under 50A circuit rating provided the cooker unit switch is within 2m of both appliances.
Also you need twin core and earth not 3 core. You won't be able to get 2x10mm in a typical Cooker unit terminal. So the final tails will probably need to be 6mm.
Due to their size I'd consider getting a pro to check your system over. Do you have an eclectic shower as well?
No - he's probably got one that only does showering....