when wiring up a new electric oven which is on its own MCB (which was isolated), i found that when i cut into the cable at the length i wanted, it tripped out the RCD. when continuity tested with test meter, i found continuity between earth and neutral. Is this what you would expect to find and can anybody explain why i am getting continuity between earth and neutral?

Thanks
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
flameport

from United Kingdom

Joined: 10 Mar 2007
Posts: 3900
Location: Bournemouth,
United Kingdom
Thanked: 609 times

PostPosted: Sat Sep 12, 2009 6:30 pm Reply with quote

Even with the MCB off, earth and neutral are still connected. Your RCD is designed to operate when there is a N-E fault within your installation, such as you cutting through a cable.

In most installations, E & N are connected together in one or more places - the supplier cutout, in the road outside, or at the substation supplying your property.
Back to top
The following user says thank you to flameport for this useful post:
martz (12 Sep 2009)
 Alert Moderators
Guitarguy

from United Kingdom

Joined: 26 Mar 2009
Posts: 177
Location: Wiltshire,
United Kingdom
Thanked: 8 times

PostPosted: Sat Sep 12, 2009 6:34 pm Reply with quote

if the house is on a PME supply, the neutral and earth is one conductor in the supply cable and both the neutral and earth tails go into the neutral side of the electricity companies cutout. That would explain continuity
Back to top
The following user says thank you to Guitarguy for this useful post:
martz (12 Sep 2009)
 Alert Moderators
cantab

from United Kingdom

Joined: 11 Sep 2009
Posts: 38
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Sep 12, 2009 6:47 pm Reply with quote

EDIT: What I wrote in this post is WRONG, so ignore it. Others have explained why.

If the RCD tripped when you cut the cable then I reckon that cable was LIVE, and you're lucky to be (a)live yourself.

I'm no spark, but I think RCDs trip if there's a current imbalance between live and neutral. A dead circuit should have zero current in both.


Last edited by cantab on Sat Sep 12, 2009 7:06 pm, edited 2 times in total
Back to top
 Alert Moderators
londonboy

from United Kingdom

Joined: 22 Feb 2009
Posts: 1577
Location: London,
United Kingdom
Thanked: 147 times

PostPosted: Sat Sep 12, 2009 6:49 pm Reply with quote

If it was live he woulda known about it!! N to E caused fault.
Back to top
 Alert Moderators
cantab

from United Kingdom

Joined: 11 Sep 2009
Posts: 38
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Sep 12, 2009 6:55 pm Reply with quote

Can you explain? Sorry, I'm a bit confused here. Am I wrong in how an RCD works?

If a circuit's dead, there should be no current flowing in either live or neutral, right. Thus, shorting neutral to earth, still no current. Am I missing something?

(EDIT: You're right that if one cuts through a live cable that should be very obvious. I'm just trying to see how cutting a dead cable would cause anything to trip.)
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 45103
Location: London,
United Kingdom
Thanked: 1592 times

PostPosted: Sat Sep 12, 2009 7:00 pm Reply with quote

cantab wrote:
If the RCD tripped when you cut the cable then I reckon that cable was LIVE,




Quote:
and you're lucky to be (a)live yourself.



Quote:
I'm no spark

Back to top
The following user says thank you to ban-all-sheds for this useful post:
Steve (12 Sep 2009)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 45103
Location: London,
United Kingdom
Thanked: 1592 times

PostPosted: Sat Sep 12, 2009 7:02 pm Reply with quote

cantab wrote:
If a circuit's dead, there should be no current flowing in either live or neutral, right. Thus, shorting neutral to earth, still no current. Am I missing something?

Yes - the fact that all the neutrals (on the RCD side) are connected together at the CU, so shorting one of them to earth shorts all of them....
Back to top
The following 2 users say thank you to ban-all-sheds for this useful post:
martz (12 Sep 2009), cantab (12 Sep 2009)
 Alert Moderators
BS3036

from United Kingdom

Joined: 24 Sep 2007
Posts: 666
Location: United Kingdom
Thanked: 19 times

PostPosted: Sat Sep 12, 2009 7:05 pm Reply with quote

As flameport mentioned, the MCB doen't switch off the neutral. The neutral will have a small voltage on it caused by current flowing through the (small) resistance of some part of the neutral cable. So if you join neutral to earth through a very small resistance it is easy for between 15 and 30 mA or more to flow from neutral (and not in the live), ie enough to trip the RCD.

Oh well. icon_smile.gif


Last edited by BS3036 on Sat Sep 12, 2009 7:07 pm, edited 2 times in total
Back to top
The following 2 users say thank you to BS3036 for this useful post:
martz (12 Sep 2009), cantab (12 Sep 2009)
 Alert Moderators
cantab

from United Kingdom

Joined: 11 Sep 2009
Posts: 38
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Sep 12, 2009 7:06 pm Reply with quote

Ah, I see. Thanks.
Back to top
 Alert Moderators
Johnmelad502

from United Kingdom

Joined: 23 Aug 2008
Posts: 2923
Location: Cumbria,
United Kingdom
Thanked: 49 times

PostPosted: Sat Sep 12, 2009 7:58 pm Reply with quote

ban-all-sheds wrote:
cantab wrote:
If the RCD tripped when you cut the cable then I reckon that cable was LIVE,




Quote:
and you're lucky to be (a)live yourself.



Quote:
I'm no spark



Wow, that was sooooooooo helpful. icon_mad.gif
Back to top
 Alert Moderators
davelx

from United Kingdom

Joined: 26 Sep 2006
Posts: 1102
Location: London,
United Kingdom
Thanked: 51 times

PostPosted: Sun Sep 13, 2009 9:11 am Reply with quote

What BAS is saying is that unless you KNOW what you are talking about then better to keep quiet and learn from those who do.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 45103
Location: London,
United Kingdom
Thanked: 1592 times

PostPosted: Sun Sep 13, 2009 3:06 pm Reply with quote

Not necessarily - sometimes doing or saying something that makes you look a right plonker can be a spur to learning things so as not to look a plonker again..
Back to top
 Alert Moderators
cantab

from United Kingdom

Joined: 11 Sep 2009
Posts: 38
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Sep 13, 2009 3:46 pm Reply with quote

Indeed icon_redface.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 45103
Location: London,
United Kingdom
Thanked: 1592 times

PostPosted: Sun Sep 13, 2009 4:07 pm Reply with quote

My words were a bit ill-chosen - I didn't think that your mistaken post made you look a "right plonker" - that's definitely too excessive - sorry about that....
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Demand in Scotland for Electrical Testing 3 600 Wed Mar 12, 2008 8:51 am
Electrical Testing 3 600 Fri Aug 26, 2005 8:07 am
ELECTRICAL TESTING 3 520 Sun May 13, 2007 8:14 pm
any good books on domestic electrical testing 8 1080 Sat Aug 05, 2006 11:30 am
My disagreement with LABC re testing of electrical work... 25 1580 Tue Jul 22, 2008 11:33 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.