New ceiling light fitted.....now RCB tripping


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
kevinyork

from United Kingdom

Joined: 16 Aug 2006
Posts: 3
Location: Yorkshire,
United Kingdom

PostPosted: Fri Jan 15, 2010 7:57 pm Reply with quote

Got a new house. Had an electrician install a BIG ceiling light this week and I mean big. Its a 20 x 20w spiral with an inbuilt transformer. Looks superb but a couple of times when turning it on the RCB for that circuit trips. It resets ok but not sure what the problem is. Any advice please?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36241
Location: Hampshire,
United Kingdom
Thanked: 1288 times

PostPosted: Fri Jan 15, 2010 8:01 pm Reply with quote

RCB is wrong

do you mean MCB?

Or RCD?

What is printed on it?
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 444
Location: Staffordshire,
United Kingdom
Thanked: 22 times

PostPosted: Fri Jan 15, 2010 8:25 pm Reply with quote

Chances are if is a fitting with low voltage lamps and a transformer in it then your electrician has not taken into account the surge on a circuit containing a transformer. Get him back and subject to the maximum EFLI values being acceptable he needs to change the MCB to a C type to overcome this problem. If its the rcd that is tripping chances are he has pinched a cable or something when installing it.

Nick
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46782
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Sat Jan 16, 2010 2:17 am Reply with quote

sparkydude wrote:
If its the rcd that is tripping chances are he has pinched a cable or something when installing it.

kevinyork wrote:
It resets ok

Who's the regular here with the animated GIF smiley of a dude in a hat slowly shaking his head?
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 444
Location: Staffordshire,
United Kingdom
Thanked: 22 times

PostPosted: Sat Jan 16, 2010 6:26 am Reply with quote

Chances are that as expected Ban all Sheds will give a sarcastic good for nothing unhelpful answer to a question he has no real knowledge about. The OP has not come back to confirm if it is an RCD or MCB yet you jump on the bandwagon AGAIN to criticise the oppinons of a tradesman . Who is to say the rcd is not faulty if it actualy is an RCD. If you cannot post a helpful reply to the OP question may i kindly suggest you keep your sarcasm to yourself.
Back to top
 Alert Moderators
Jacobssi

from United Kingdom

Joined: 03 Jan 2010
Posts: 135
Location: Berkshire,
United Kingdom

PostPosted: Sat Jan 16, 2010 8:14 am Reply with quote

What is elfi?
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17401
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Sat Jan 16, 2010 9:17 am Reply with quote

Jacobssi wrote:
What is elfi?

You mean EFLI
Earth Fault Loop Impedance
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
Jacobssi (16 Jan 2010)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46782
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Sat Jan 16, 2010 11:28 am Reply with quote

sparkydude wrote:
The OP has not come back to confirm if it is an RCD or MCB yet you jump on the bandwagon AGAIN to criticise the oppinons of a tradesman .

The OP has not come back to confirm if it is an RCD or MCB yet you have decided, if it is an RCD, to criticise the work of a tradesman.


Quote:
Who is to say the rcd is not faulty if it actualy is an RCD.

You, as in "If its the rcd that is tripping chances are he has pinched a cable or something when installing it", rather than "If its the rcd that is tripping chances are that it is faulty".


Quote:
If you cannot post a helpful reply to the OP question may i kindly suggest you keep your sarcasm to yourself.

I'm not sure how helpful your reply was to tell the OP that if it's an RCD that's tripping it's probably due to an intermittent earth fault when you think that the RCD might be faulty.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
ceiling fitted down light kit 2 320 Tue Dec 11, 2007 1:37 pm
FITTED NEW LIGHT AND SWITCH,HIT A PROBLEM 5 660 Tue Jul 10, 2007 9:58 pm
New light fixture fitted (with pics) not working 22 660 Sun May 01, 2011 5:38 pm
New light fitted but not working (photo's attached) 11 300 Mon Jan 06, 2014 7:20 pm
Fitted dimmer and now light doesnt work 9 220 Mon Aug 05, 2013 10:57 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.