MZAID

from United Kingdom

Joined: 15 Apr 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 3:58 pm    Post Subject:
CONSUMER UNIT
Reply with quote Thanks

I notice that the wiring system at my premise is old. I want to change the old fuse box to modern consumer unitand rewire the house. I notice that the supplier fuse unit is opened. Can I pull out the supplier\\\'s fuse myself before i start the work?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 4:52 pm    Post Subject:
Re: CONSUMER UNIT
Reply with quote Thanks

MZAID wrote:
I notice that the wiring system at my premise is old. I want to change the old fuse box to modern consumer unitand rewire the house. I notice that the supplier fuse unit is opened. Can I pull out the supplier\\\'s fuse myself before i start the work?


full re-wire is NOT for DIYers. if you do pull the fuse, take the fuse out of the holder and put holder back in just so you cant accidently touch anything inside.
Back to top
 Alert Moderators
felix

from United Kingdom

Joined: 23 Jan 2005
Posts: 900
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 6:46 pm    Post Subject:
Reply with quote Thanks

Whoever broke the seal on that fuse also broke the law. Have a close look at the meter. They might have tampered with that as well. Now what I'm thinking is this. If you end up getting 'the electricity board' (or whatever they call themselves in your area) to come and finish the job around the meter, will they find your fingerprints all over it?
Back to top
 Alert Moderators
has

from United Kingdom

Joined: 27 Mar 2005
Posts: 60
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 8:20 pm    Post Subject:
Reply with quote Thanks

You really should not be touching the cut out fuse, but if you do at as I suspect you will, at least make sure everything is turned off first at your consumer unit.
Back to top
 Alert Moderators
scoobydooby

from United Kingdom

Joined: 11 Apr 2005
Posts: 49
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 9:09 pm    Post Subject:
Reply with quote Thanks

if he cant pull out the cut out fuse, how is he supposed to carry out the work??
Back to top
 Alert Moderators
PowerTool

from United Kingdom

Joined: 21 Dec 2004
Posts: 192
Location: Durham,
United Kingdom
Thanked: 0 times

PostPosted: Fri Apr 15, 2005 9:15 pm    Post Subject:
Reply with quote Thanks

I guess it is a reference to the dreaded Part P,rather than anything else (the "thou shalt not work on your own electrics - get an electrician in" clause icon_eek.gif )

__________________
HAMMER ACTION - when all else fails..
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Sun Apr 17, 2005 2:05 am    Post Subject:
Reply with quote Thanks

i do wonder what would happen if you reinserted a cut out fuse against a dead short icon_twisted.gif
Back to top
 Alert Moderators
felix

from United Kingdom

Joined: 23 Jan 2005
Posts: 900
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 17, 2005 3:09 pm    Post Subject:
Reply with quote Thanks

Quote:
i do wonder what would happen if you reinserted a cut out fuse against a dead short


I did that once with a 5 amp fuse. Stupid mistake; light switch fixing bolt tightened onto live wire. It was a very big bang! I shudder to think what a 100 amp jobby would do.

MZAID, if you must tangle with that fuse, make sure every single switch in your new consumer unit is OFF - and triple check everything on the meter side of the main isolator - before you put it back in.
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 17, 2005 3:58 pm    Post Subject:
Reply with quote Thanks

Do not pull the Service Fuse unless you remove the fuse from it's holder and replace this in the cut-out whilst undertaking any work.

Depending on the type of cutout you have, the bottom terminals may not be shielded, and these will remain live at all times. They do not have a fuse backing them that would protect you if you touched the terminals, and any shock here stands a good chance of being fatal

If you need a full rewire, I would suggest that you get a sparky in to do it. Part P requires that this work is notified to your local building control and that they agree it first, this will cost you money, then you will need to get a registered spark in to test the installation when you have completed the work, again this will cost. Then you will need the Local Building Control to come out and inspect, again this will cost (Your up to about £700 so far).

Any deviations/faults will need to be corrected before the installation would pass muster, and this could mean subsequent visits from the sparky, the Building control, or both, and that will be additional cost.

In the long run, you will be better off getting in a registered spark who can self certify the work, it will be quicker, and in the long run, cheaper.

Now I'll drink my tea and wait for the flaming to start.

__________________
I only do commercial and Industrial so Prescott can shove his Part P tax
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 17, 2005 4:00 pm    Post Subject:
Reply with quote Thanks

plugwash wrote:
i do wonder what would happen if you reinserted a cut out fuse against a dead short icon_twisted.gif


With a 100A fuse Plug you could be blinded by the flash, have severe burns to your hand, be showered with molten ceramic material and/or metal fragment depending on how bad the short was.

I have seen the aftermath of a 100A cutout blowing up....looked like a small grnade had been detonated, and I am not exagerating.

__________________
I only do commercial and Industrial so Prescott can shove his Part P tax
Back to top
 Alert Moderators
MZAID

from United Kingdom

Joined: 15 Apr 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Apr 18, 2005 9:28 am    Post Subject:
Reply with quote Thanks

FWL_Engineer wrote:
Do not pull the Service Fuse unless you remove the fuse from it's holder and replace this in the cut-out whilst undertaking any work.

Depending on the type of cutout you have, the bottom terminals may not be shielded, and these will remain live at all times. They do not have a fuse backing them that would protect you if you touched the terminals, and any shock here stands a good chance of being fatal

If you need a full rewire, I would suggest that you get a sparky in to do it. Part P requires that this work is notified to your local building control and that they agree it first, this will cost you money, then you will need to get a registered spark in to test the installation when you have completed the work, again this will cost. Then you will need the Local Building Control to come out and inspect, again this will cost (Your up to about £700 so far).

Any deviations/faults will need to be corrected before the installation would pass muster, and this could mean subsequent visits from the sparky, the Building control, or both, and that will be additional cost.

In the long run, you will be better off getting in a registered spark who can self certify the work, it will be quicker, and in the long run, cheaper.

Now I'll drink my tea and wait for the flaming to start.
Back to top
 Alert Moderators
HDRW

from United Kingdom

Joined: 28 Feb 2005
Posts: 273
Location: Hertfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Apr 18, 2005 10:59 am    Post Subject:
Reply with quote Thanks

felix wrote:
Whoever broke the seal on that fuse also broke the law.

So how does a professional sparky replace a consumer unit? I rang and asked my supplier if they would fit an isolator between the meter and the CU, and (eventually) they said: "Get a local electrician to do it".

When I asked if they would have to come out to unseal the service fuse, they said "Oh no, the electrician will do that".

So is there something pre-part-P that gives an electrician rights that a DIYer doesn't have in this case?

Cheers,

Howard

__________________
How much of a burning smell should I be getting? icon_eek.gif
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Mon Apr 18, 2005 2:45 pm    Post Subject:
Reply with quote Thanks

many of them just pull the bloody fuse and get on with it

you/they aren't techincally supposed to do it (at least not without permission and you are unlikly to get permission in writing) but to be totally honest unless they see evidence of trying to steal leccy they don't seem to care
Back to top
 Alert Moderators
RodMoore

from United Kingdom

Joined: 16 Jun 2008
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 16, 2008 9:20 am    Post Subject:
Reply with quote Thanks

I agree, that's how i understand it too- they're only interested if you're trying to "by-pass" the meter.

I also totally agree with the point about making sure everything is OFF when you come to re-insert the main fuse.

I liked the "small hand grenade" story- have a look on youtube for video of dead shorts... search for "electric arc"
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Jun 16, 2008 10:21 am    Post Subject:
Reply with quote Thanks

Welcome to the forum, Rod.

Please don't take it too hard when you get told off for replying to a post that's over 3 years old....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replacing CONSUMER UNIT queries 6 780 Fri Nov 02, 2007 6:47 pm
consumer unit mounting 2 640 Sat Nov 03, 2007 9:12 pm
Garage Consumer Unit Supply 3 580 Mon Nov 05, 2007 3:16 pm
consumer unit getting hot 10 420 Fri Nov 02, 2007 1:25 pm
Consumer unit fuseway / ring-main 33 1620 Fri Nov 02, 2007 12:54 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.