introduce Honeywell BDR91A Relay to Potterton EP2002 timer

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Sun Oct 31, 2010 8:22 pm Reply with quote

Hi there,

My Alpha boiler in the loft has no internal timer clock or room thermostat connected. The timer is an upstairs bedroom and I have bought a DT92E Wireless Room Thermostat for downstairs.

Please could someone help me with the wiring configueration so these will work together.

Potterton is currently connected:
Mains: Blue N & Brown L

To boiler: Blue N & Brown L, Black 2 & 4 and Red jumper between L & 5. It also has open connections available for A,B,C,D.

The BDR91A Relay has open connections for NLL and ABC.

Your help will be truly appreciated.

Many thanks,
Andy
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Sun Oct 31, 2010 8:56 pm Reply with quote

Blueandy197 wrote:
To boiler: Blue N & Brown L, Black 2 & 4 and Red jumper between L & 5.

I can understand the black from 4 to the boiler as that is CH ON, but normally 2 is not used as that is CH OFF.

Can you check this please. If it is there, can you find what it connects to at the boiler (boiler details will be helpful as well).
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Sun Oct 31, 2010 9:53 pm Reply with quote

Thanks for taking an interest!

It'a an Alpha Combi Boiler CB28.

The Potterton timer has black in both 2 & 4, but 1 & 3 are empty.

Up at the boiler both black go in to 1 & 2 of a connection block marked 'room thermostat' and lead out as two red wires that diappear in to the main housing.

On the back of the housing there is a wiring diagram that says 'remove link to connect external control to connect switched live to no. 1 terminal', connect external control to terminals 1 & 2.

Cheers
Andy
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Mon Nov 01, 2010 10:38 am Reply with quote

Blueandy197 wrote:
It's an Alpha Combi Boiler CB28.

The Potterton timer has black in both 2 & 4, but 1 & 3 are empty.

Whoever wired it up originally did not know what they are doing.

1 & 3 empty is OK because they are the HW terminals which are not required as you have a combi.

A wires is needed in terminal 4 as it is the Heating ON terminal, but a wire is not needed in terminal 2. Did the boiler run continuously?

The Relay box needs to be wired as follows:

Connect one L and N to a permanent mains supply, e.g the L and N terminals of the EP2002.

Remove link between L and 5 on EP2002
Connect EP2002 terminal 4 to Relay Terminal A
Connect Relay terminal B to boiler terminal 1.
Connect EP2002 terminal 5 to boiler terminal 2
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Mon Nov 01, 2010 11:38 am Reply with quote

Ex-girlfriends 2nd cousin was a gas fitter?

Thank you so much for your post I hope to try this tonight.

Andy
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Mon Nov 01, 2010 11:48 am Reply with quote

Blueandy197 wrote:
Ex-girlfriends 2nd cousin was a gas fitter?

Some gas fitters are either not qualified for or do not understand the electrical side of heating and hot water systems. So they employ an electrician, who may be qualified but also does not understand.
Back to top
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Mon Nov 01, 2010 5:55 pm Reply with quote

D_Hailsham wrote:
Blueandy197 wrote:
Ex-girlfriends 2nd cousin was a gas fitter?

Some gas fitters are either not qualified for or do not understand the electrical side of heating and hot water systems. So they employ an electrician, who may be qualified but also does not understand.


never a truer word said Mr H
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Tue Nov 02, 2010 9:54 pm Reply with quote

Evening guys,

I've re-wired per your advice and have the wireless room stat talking to the relay, but cannot get the boiler to fire up even on override to CH constant.

Any thoughts?

Thank you
Andy
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Wed Nov 03, 2010 10:04 am Reply with quote

Blueandy197 wrote:
I've re-wired per your advice and have the wireless room stat talking to the relay, but cannot get the boiler to fire up even on override to CH constant.

Try swapping the wires to boiler 1 and 2.

If that does not work, do you have a multimeter? If so check the voltage at between boiler terminal 1 and N and between 2 and N. One of them should be 240Vac, even when the relay is off; the other when the relay is on.
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Wed Nov 03, 2010 12:05 pm Reply with quote

I did swap the wires over, but will check the weekend with a multimeter as my dad has mine and will let you know it that's okay.

Out of interest what is Terminal 5 for?

Have a great week
Andy
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Wed Nov 03, 2010 12:35 pm Reply with quote

Blueandy197 wrote:
Out of interest what is Terminal 5 for?

It's the common for the heating switch. When CH is ON, 5 connects to 4; when CH is OFF, 5 connects to 2.

5 get its supply from boiler terminal 2 (which should be permanent 240Vac). When the timer turns CH ON, 5 connects to 4, which is connected to Relay terminal A. When the relay closes, A connects to B, which is connected to boiler Terminal 1, the switched live terminal.
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Wed Nov 03, 2010 10:52 pm Reply with quote

Evening, I've been up in the loft with my multimeter and boiler terminal 2 was 240v and terminal 1 was 0v when I then went downstairs to re-wire the EP2002 as I had took everything out last night.

After re-wiring I still could not get it to work and now even more at a loss as on the EP terminal 5 connected to boiler T2 is 0v and Relay terminal B connected boiler T1 is 110v.

I went back in to the loft T1 is indeed now 110v and T2 still 240v.

Nothing changed when I flicked the Relay on/off.

Any ideas?

Kind regards,
Andy
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8555
Location: Sussex,
United Kingdom
Thanked: 984 times

PostPosted: Thu Nov 04, 2010 10:26 am Reply with quote

Blueandy197 wrote:
Boiler terminal 2 was 240v and terminal 1 was 0v

That's correct: 2 is the supply and 1 the switched live.

Quote:
the EP terminal 5 connected to boiler T2 is 0v

Then EP T5 cannot be connected to boiler T2.

Are you using the pair of black wires to connect the boiler to the relay? If so,try swapping them over at both ends to see if the other one gives 240v on 5. If it does the other wire must be broken. If it is, there is a way round it, as follows:

Connect one L and N to a permanent mains supply, e.g the L and N terminals of the EP2002. Already done

Replace link between L and 5 on EP2002 New
Connect EP2002 terminal 4 to Relay Terminal A Already done
Connect Relay terminal B to boiler terminal 1. Use the "good" wire

There is no need now for the wire from Boiler T2 to 5.
Back to top
 Alert Moderators
Blueandy197

from United Kingdom

Joined: 31 Oct 2010
Posts: 7
Location: United Kingdom

PostPosted: Thu Nov 04, 2010 10:18 pm Reply with quote

It works, it works, it works. Thank you so much, they say winter is coming next week!

I was using the two black wires originally as you said and had swapped them over every which way. Tonight I used your work around, but picked up the one of the black wires at random at the wiring centre as couldn't remember where I'd left them at the boiler last night T1 or T2.

So I replaced the link between L and 5 and first time lucky.

For future reference what just happened and what is the difference in this configueration that wouldn't/shouldn't be as the initial we first tried as the preferred method - are they both just as okay?

Again you are genius!

Andy
Back to top
 Alert Moderators
DP

from United Kingdom

Joined: 10 Dec 2003
Posts: 6468
Location: Glasgow,
United Kingdom
Thanked: 725 times

PostPosted: Fri Nov 05, 2010 7:36 am Reply with quote

Perhaps I am missing a vital piece of information here.

Boiler is a combi wired to a potterton timer that is to be replaced with a honeywell wireless programmer.

Why not remove the potty programmer, wire the live and neutral to L and N, and two blacks to A and B?

Did I also see a note that live needs to be taken to the relay contacts? The switching is better left as voltage free (always unless otherwise stated) as parts of circuit would be live when boiler switched off at the facia controls
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
How to introduce x400 to a sealed system 5 120 Thu Jan 13, 2011 8:00 pm
Replace existing wall timer with evotouch relay BDR91 6 100 Wed Oct 23, 2013 1:59 pm
Ferroli Optima Honeywell VMF7 PCB Relay Fault 8 580 Sat Mar 27, 2010 7:01 pm
Connecting a Honeywell BDR91 Relay Box to a Baxi 105 HE 3 80 Sun Feb 23, 2014 11:48 pm
Honeywell HC60NG wireless relay unit replacement - help 7 2920 Sun Oct 14, 2007 6:52 pm


 