Hello,

Would be grateful for people opinions on this situation I am in....

The Client has requested a 17th edition consumer unit upgrade due to a child receiving an electric In the house. I visited the house to get an idea of what's going on etc.. the gas and water main have a 6mm earth tagged onto them. However, the client has limited funds and can only afford a fuseboard change including testing. Will take an extra day to upgrade the bonding to 10mm as laminate flooring/concrete floors are everywhere! With the supply characteristics that's present, would I be able to leave it at 6mm. Tncs system, main fuse 60a 1361. Or could I put it as a limitation on the certificate? Upgrade of equipotential bonding to water main and gas main in 10mm could not be carried out at present???

Carl
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Thu May 12, 2011 10:02 am Reply with quote

..


Last edited by holmslaw on Mon Apr 09, 2012 9:58 pm, edited 1 time in total
Back to top
 Alert Moderators
Carloss

from United Kingdom

Joined: 31 Mar 2004
Posts: 168
Location: United Kingdom

PostPosted: Thu May 12, 2011 10:06 am Reply with quote

Thanks, sorry for sloppy posting, using my phone to write this!

Would it be acceptable if I carried out a continuity check on the bonding if I get readings below 0.05ohms would be acceptable? taking into consideration the type of earthing system and fuse size?

Thanks,
Carl
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Thu May 12, 2011 10:11 am Reply with quote

..


Last edited by holmslaw on Mon Apr 09, 2012 9:59 pm, edited 1 time in total
Back to top
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Thu May 12, 2011 5:26 pm Reply with quote

holmslaw wrote:
Yes you should test is as part of the cu change, but it will still be unacceptable because the conductors are too small.
.

They may be ok if the system is TT
Back to top
 Alert Moderators
londonboy

from United Kingdom

Joined: 22 Feb 2009
Posts: 1579
Location: London,
United Kingdom
Thanked: 148 times

PostPosted: Thu May 12, 2011 5:55 pm Reply with quote

The installation is TNCS.

I beleive you can verify 6mm by using adabatic equation.
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Thu May 12, 2011 5:55 pm Reply with quote

..


Last edited by holmslaw on Mon Apr 09, 2012 9:59 pm, edited 1 time in total
Back to top
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Thu May 12, 2011 5:58 pm Reply with quote

holmslaw wrote:
matt1e wrote:
holmslaw wrote:
Yes you should test is as part of the cu change, but it will still be unacceptable because the conductors are too small.
.

They may be ok if the system is TT


Carloss wrote:
Tncs system,


icon_smile.gif


icon_redface.gif

allright I'll go and clean me specs icon_lol.gif
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Thu May 12, 2011 6:01 pm Reply with quote

..


Last edited by holmslaw on Mon Apr 09, 2012 10:00 pm, edited 1 time in total
Back to top
 Alert Moderators
ebee

from United Kingdom

Joined: 14 Aug 2005
Posts: 1699
Location: Lancashire,
United Kingdom
Thanked: 29 times

PostPosted: Fri May 13, 2011 8:39 am Reply with quote

TNC-S (PME) requires 10mm min (even then your supplier might require more)
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Earth bonding at water pipes 2 100 Sat Feb 02, 2013 5:26 pm
Earth Bonding - Separate cables for Water and Gas Pipes ? 9 5260 Mon Apr 24, 2006 9:00 am
Water Mains - Bonding - SubMain Earth 15 1340 Mon Feb 18, 2008 5:31 pm
Help - - -Earth Bonding on water main (part plastic ) 4 540 Tue Jul 15, 2008 9:15 am
main earth bonding to water and gas 5 140 Sat Sep 10, 2011 3:36 pm


 