Carloss

Joined: 31 Mar 2004 Posts: 168 Location: United Kingdom
|
Posted: Thu May 12, 2011 9:53 am |
|
|
Hello,
Would be grateful for people opinions on this situation I am in....
The Client has requested a 17th edition consumer unit upgrade due to a child receiving an electric In the house. I visited the house to get an idea of what's going on etc.. the gas and water main have a 6mm earth tagged onto them. However, the client has limited funds and can only afford a fuseboard change including testing. Will take an extra day to upgrade the bonding to 10mm as laminate flooring/concrete floors are everywhere! With the supply characteristics that's present, would I be able to leave it at 6mm. Tncs system, main fuse 60a 1361. Or could I put it as a limitation on the certificate? Upgrade of equipotential bonding to water main and gas main in 10mm could not be carried out at present???
Carl |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Thu May 12, 2011 10:02 am |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 9:58 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
Carloss

Joined: 31 Mar 2004 Posts: 168 Location: United Kingdom
|
Posted: Thu May 12, 2011 10:06 am |
|
|
Thanks, sorry for sloppy posting, using my phone to write this!
Would it be acceptable if I carried out a continuity check on the bonding if I get readings below 0.05ohms would be acceptable? taking into consideration the type of earthing system and fuse size?
Thanks,
Carl |
|
| Back to top |
|
|
|
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Thu May 12, 2011 10:11 am |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 9:59 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
matt1e

Joined: 13 Dec 2008 Posts: 1954 Location: Tyne and Wear, United Kingdom Thanked: 206 times
|
Posted: Thu May 12, 2011 5:26 pm |
|
|
| holmslaw wrote: | Yes you should test is as part of the cu change, but it will still be unacceptable because the conductors are too small.
. |
They may be ok if the system is TT |
|
| Back to top |
|
|
|
|
|
 |
londonboy

Joined: 22 Feb 2009 Posts: 1576 Location: London, United Kingdom Thanked: 146 times
|
Posted: Thu May 12, 2011 5:55 pm |
|
|
The installation is TNCS.
I beleive you can verify 6mm by using adabatic equation. |
|
| Back to top |
|
|
|
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Thu May 12, 2011 5:55 pm |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 9:59 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
matt1e

Joined: 13 Dec 2008 Posts: 1954 Location: Tyne and Wear, United Kingdom Thanked: 206 times
|
Posted: Thu May 12, 2011 5:58 pm |
|
|
| holmslaw wrote: | | matt1e wrote: | | holmslaw wrote: | Yes you should test is as part of the cu change, but it will still be unacceptable because the conductors are too small.
. |
They may be ok if the system is TT |
 |
allright I'll go and clean me specs  |
|
| Back to top |
|
|
|
 |
holmslaw

Joined: 12 Dec 2006 Posts: 5844 Location: Vanuatu Thanked: 400 times
|
Posted: Thu May 12, 2011 6:01 pm |
|
|
..
Last edited by holmslaw on Mon Apr 09, 2012 10:00 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
ebee

Joined: 14 Aug 2005 Posts: 1621 Location: Lancashire, United Kingdom Thanked: 28 times
|
Posted: Fri May 13, 2011 8:39 am |
|
|
TNC-S (PME) requires 10mm min (even then your supplier might require more) |
|