Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Brad77

from United Kingdom

Joined: 31 Mar 2011
Posts: 4
Location: Nottingham,
United Kingdom

PostPosted: Tue May 31, 2011 2:21 pm Reply with quote

I've just got a shower, its 8.5KW.

Our consumer unit is very old, its a MEM Memera21.

Currently its got 2x 5A MCBs for lights, 16A for Immersion Heater, 32A for power sockets and 32A for the cooker.
The cooker wire goes into a big switch on the wall behind the cooker and inside this theres another wire that goes off in the wall up to the airing cupboard upstairs which is behind where the shower will go, here there is another switch like you'd have for a cooker.

So I know the shower should ideally be on a seperate MCB and wire, but I'm wondering if it'd be safe to use this existing wire. It obviously used to be for a shower before we bought the house but no idea what power rating that was.

I've seen the maths of 8500W/230v = 36.96A
So I think I'll need to change the MCB from 32A to a 40A (or rather I'll be getting an electrician in to swap this).

The MCBs already in use are Type1,
I've found a Type3 (http://www.reconelectrical.co.uk/index.php?act=viewProd&productId=27527)
and I found a TypeB (http://www.neweysonline.co.uk/mem-mcb-memshield-type-b-40a-single-pole-230v-ac/1050072404/ProductInformation.raction)
Are these any good for this CU?
The only place I've found a Type1 MCB is on ebay for 30+postage, I'm trying to do this a cheaply as possible.

Thanks,
Brad.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12598
Location: Oxfordshire,
United Kingdom
Thanked: 1046 times

PostPosted: Tue May 31, 2011 3:05 pm Reply with quote

Brad77 wrote:


So I know the shower should ideally be on a seperate MCB and wire, but I'm wondering if it'd be safe to use this existing wire.


It is not a matter of "ideally" - it is essential. You cannot share the circuit for the cooker with the shower. Period.
You will need a omplete new circuit from the CU to the shower.


Also, you will need to protect the shower circuit with an RCD and provide an isolation switch in/near the bathroom.
Also this is notifiable work. So, unless you are competent with electrical work, you need a registered electrician to do this work for you.

See http://www.diynot.com/wiki/electrics:part_p:diy_electrical_work_and_the_law for details
Back to top
The following user says thank you to Taylortwocities for this useful post:
Brad77 (1 Jun 2011)
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Tue May 31, 2011 3:39 pm Reply with quote

..


Last edited by holmslaw on Tue Apr 10, 2012 9:06 am, edited 1 time in total
Back to top
The following user says thank you to holmslaw for this useful post:
Brad77 (1 Jun 2011)
 Alert Moderators
bernardgreen

from United Kingdom

Joined: 03 Nov 2006
Posts: 10760
Location: Bedfordshire,
United Kingdom
Thanked: 828 times

PostPosted: Tue May 31, 2011 4:09 pm Reply with quote

Brad77 wrote:
I'm trying to do this a cheaply as possible.


Money can be replaced, a life lost cannot be replaced.
Back to top
The following user says thank you to bernardgreen for this useful post:
Brad77 (1 Jun 2011)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48200
Location: London,
United Kingdom
Thanked: 1809 times

PostPosted: Tue May 31, 2011 5:02 pm Reply with quote

Brad77 wrote:
I'll be getting an electrician in to swap this

Use him to get a proper job done, with a new circuit, a new MCB, testing and certifications regarding electrical and building regulations compliance.

You won't find anybody competent who is prepared to do what you want anyway.
Back to top
The following user says thank you to ban-all-sheds for this useful post:
Brad77 (1 Jun 2011)
 Alert Moderators
Brad77

from United Kingdom

Joined: 31 Mar 2011
Posts: 4
Location: Nottingham,
United Kingdom

PostPosted: Wed Jun 01, 2011 9:57 am Reply with quote

Thanks for all the replies guys.

I was hoping for an answer like: "it's not ideal but will probably be ok", i.e. the cheapest answer.
But honestly I was expecting answers like you've all given.

My CU has a black piece of plastic to the left of the MCBs, I'm hoping this can be removed to allow another MCB to be installed.

If I buy an MCB, pull up carpets and floorboards and lay a 10mm cable. Then disconnect the wire in the airing cupboard switch, and also disconnect it in the cooker switch.
Then get an electrician in to wire it all up, is that something they'd do?
Or would they insist on laying the cable themselves and buying all the parts themselves?

oh and I forgot I need an RCD, not sure where that goes, another task for an electrician.
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Wed Jun 01, 2011 10:26 am Reply with quote

..
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
New shower - which type? 13 7300 Thu Mar 22, 2007 9:17 am
MCB size and type required for a 10.8kW electric shower 6 3840 Sun Feb 10, 2008 6:32 pm
type of fan acceptable in a shower 5 120 Mon Nov 21, 2011 11:40 pm
What Type of Shower Light ? 13 900 Mon Feb 27, 2006 9:47 am
Replace old consumer unit with new RCD type 4 420 Fri Sep 10, 2010 12:05 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.