Air in Hot water cylinder

This topic originated from the How to page called Problems associated with noises from the central heating system
Click here to return to the page called Problems associated with noises from the central heating system.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Superwidget

from United Kingdom

Joined: 27 Sep 2003
Posts: 3
Location: United Kingdom

PostPosted: Sat Sep 27, 2003 9:30 am Reply with quote

I have completely drained my CH system to add in a new radiator, then refilled and bled all the radiators. Unfortunately, I do not have any hot water and the hot water cylinder seems to be empty / full of air. The automatic air bleed appears to be working correctly. Can anyone advise what I can do? Thanks. icon_sad.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Sat Sep 27, 2003 1:00 pm Reply with quote

What type of system do you have?
If it is a normal vented hot water tank - ie with a header tank in the loft, it is fed from this tank, and the header tank is fed from a connection to the main, you would have no need to drain it to add radiators. Is it a thermal store? Is it an unvented tank?
For an unvented tank (also no need to drain, turn on the cold water feed and turn on a hot tap. Air will come out until it is full. For a thermal store, is it a sealed system, or does it have its own header tank. Again you ould only have to drain this if it was a direct heating type, otherwise no need to drain.
Back to top
 Alert Moderators
masona

from United Kingdom

Joined: 05 Jan 2003
Posts: 12804
Location: Essex,
United Kingdom
Thanked: 110 times

PostPosted: Sat Sep 27, 2003 2:50 pm Reply with quote

Is the radiator working and are you getting water out of hot taps?

As oilman said "what type of system do you have?"
Back to top
 Alert Moderators
Superwidget

from United Kingdom

Joined: 27 Sep 2003
Posts: 3
Location: United Kingdom

PostPosted: Sat Sep 27, 2003 3:17 pm Reply with quote

I have a normal vented hot water tank - ie with a header tank in the loft, it is fed from this tank, and the header tank is fed from a connection to the main.
It's gravity-fed and does not have a motorised valve. We have bled the radiators 3 or 4 times - each time we find more air in them and the automated venting valve activates every so ooftenb when the water pump is on (i.e. partially emptying system only).
We have hot radiators but no hot water from any taps + the hot water cylinder is cold. Thanks for your responses so far - any suggestions now???
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23328
Location: Sussex,
United Kingdom
Thanked: 27 times

PostPosted: Sat Sep 27, 2003 4:31 pm Reply with quote

this will need confirmation, but i think this is one of the occasions when you put a hose on the cold tap and put the other end on the hot tap and turn them both on, but you have to have some one in the loft to make sure the expansion tank doesnt over fill. the idea is it forces all the air out of the cylinder
Back to top
 Alert Moderators
masona

from United Kingdom

Joined: 05 Jan 2003
Posts: 12804
Location: Essex,
United Kingdom
Thanked: 110 times

PostPosted: Sat Sep 27, 2003 4:32 pm Reply with quote

Sound like you have a airlock.

When the water tank empty,air got in creating a airlock.You need to get a water main pressure back up to the hot tap with a hose somehow and force the air out into the tank.If it a bath/shower mixer,I have made a connection on the shower pipe outlet with a garden hose & turn the shower lever to shower position and open up the hot tap with the cold tap shut and turn on the water main on.This way you don't get wet instead of the old method with towel. Don't do it for too long as the water level will overfill out the overflow
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23328
Location: Sussex,
United Kingdom
Thanked: 27 times

PostPosted: Sat Sep 27, 2003 4:34 pm Reply with quote

snap icon_lol.gif
Back to top
 Alert Moderators
masona

from United Kingdom

Joined: 05 Jan 2003
Posts: 12804
Location: Essex,
United Kingdom
Thanked: 110 times

PostPosted: Sat Sep 27, 2003 5:25 pm Reply with quote

ahhh, 1 minute late was I icon_exclaim.gif icon_smile.gif


Also I forgot to mention, make sure the cold storage tank is getting water + the ballcock is okay.
Back to top
 Alert Moderators
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Sat Sep 27, 2003 5:51 pm Reply with quote

Superwidget, are you getting cold water from your hot taps? If not follow breezer and masona. f you are getting cold water, then any airlock is in the heating side not the "water to tap" side. You are getting hot water to the radiators, what controls the flow to the hot water tank? Do you have 2 pumps? If not then you must have a valve or were you saying earlier that you have gravity heating to the hot water cylinder?
Back to top
 Alert Moderators
Superwidget

from United Kingdom

Joined: 27 Sep 2003
Posts: 3
Location: United Kingdom

PostPosted: Sun Sep 28, 2003 5:49 pm Reply with quote

Many thanks for all your useful suggestions. After bleeding all the radiators & activating the automatic bleed valve many times the hot water in the taps has started to work - although there still appears to be some air in the system from the noise of the pump. We have tried starting, stopping and changing the speed of the hot water pump several times which appears to have speeded up the rate of air removal by the automatic bleedvalve. Having examined the system more carefully there appear to be TWO water pumps (one in boiler & one next to hot water cylinder) and NO motorised switch over valve. One pump comes on when room heating is selected and the other pump comes on when hot water heating is selected. Is the system a little unusual as most systems in DIY plumping guides have either a switch over valve or gravity feed. Should I add a switch over valve or stay with two pumps ? Is there anything else I can do to remove trapped air or should I leave the automated bleed valve to do its job ??
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23328
Location: Sussex,
United Kingdom
Thanked: 27 times

PostPosted: Sun Sep 28, 2003 6:05 pm Reply with quote

have you tried bleeding the pump?

(just like you would a radiator, except you turn the big screw in the centre of the pump)
Back to top
 Alert Moderators
masona

from United Kingdom

Joined: 05 Jan 2003
Posts: 12804
Location: Essex,
United Kingdom
Thanked: 110 times

PostPosted: Sun Sep 28, 2003 7:30 pm Reply with quote

Bleeding the radiator will not make any difference to the hot water tap.I still say try and force the rest of the air out as in my previous post.
Back to top
 Alert Moderators
homeDIYonly

from United Kingdom

Joined: 08 Mar 2012
Posts: 7
Location: London,
United Kingdom

PostPosted: Thu Mar 08, 2012 12:17 pm Reply with quote

Hopeing for some help!

Firstly the system I have in my house - I have a main water talk in the loft, which feeds the hot water cylinder on the first floor. I have a water pump that feeds the hot water for the whole house connected off the hot water cylinder - so when any hot water tap opens the pump kicks into action.

So my issue I had a leaky hot water tap and turned the mains cold water supply off from outside my house and then emptied the water of the cylinder and main water tank in the loft. so no water was coming through my taps. I replaced the washer and then turned the water back on from the mains.

Now my hot water is not coming at all! from what I have read already there is clearly air in the system but when I try the U technique with the cold water is just stops the pump working.

Any suggestions - I am not even sure the water cylinder is full - it definately has water because I hear it filling but doubt very much its full - I think it full of air! is there a way I can air it? so the pump is not effected!

completely lost and this is now day 2 without hot water....
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 5725
Location: Essex,
United Kingdom
Thanked: 1189 times

PostPosted: Thu Mar 08, 2012 12:24 pm Reply with quote

stick to one post mate , its confusing for everyone when you post the same problem in different places.
Back to top
 Alert Moderators
Nige F

from United Kingdom

Joined: 28 Jun 2005
Posts: 16259
Location: United Kingdom
Thanked: 814 times

PostPosted: Thu Mar 08, 2012 5:27 pm Reply with quote

homeDIYonly wrote:
!

completely lost and this is now day 2 without hot water....
And Year 9 since the original post icon_mrgreen.gif
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Can Hot Water Storage Cylinder Be Used with Combi Boiler? 15 540 Sat Jan 21, 2012 12:51 am
Problems with hot water cylinder heating system - pls help 3 180 Tue Apr 12, 2011 10:49 pm
Pinholing in Hot Water Cylinder 10 560 Sun Mar 02, 2008 1:54 pm
new water cylinder fitted. are all these problems connected 12 140 Sat Mar 01, 2014 2:15 pm
Position of Hot water Cylinder and Cold water tank 6 180 Thu Apr 14, 2011 12:44 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.