You need to check that both the gas supply (assuming there is one) and the water main have 10mm2 earth wire from main earthing terminal.
The water should be bonded on the consumers side of the main stopcock, as close as possible to the cock, and the gas should be bonded also on the consumers side of the supply, no more than 300mm from meter. However, if the meter is outside, the bonding should be on the inside, close to where the pipe enters the property.
The IEE used to ask for supplementary (earth connection between metal pipes, sinks etc) bonding in the kitchen, but now they see it as a danger, so they don't recommend bonding in the kitchen anymore.
However, supplementary bonding is strong in the bathroom, where you should link water and heating pipes, metal wastes, metal baths, radiators, pipes in the airing cupboard and also link to the earth wires of electrical services within the bathroom like immersion heater, shower, shaver point, lighting, electric towel rails, fans etc. This list is not exhaustive.
This is to make all the metalwork/ earthwires the same potential ie they are all "as one".