General position
1. The terminal must not cause an obstruction nor the discharge a
nuisance. Particular care should be exercised with regards to the
pluming of the flue gases and any increase in noise levels.
2. If a terminal is fitted less than 2 metres above a surface to
which people have access, then a guard must be fitted.
A terminal protective guard is available from Tower Flue
Components, Vale Rise, Tonbridge. Tel No. (01732) 351555.
The terminal guard must be securely fixed to the wall using
suitable plugs and corrosion resistance screws. The guard must
be symmetrically positioned about the terminal assembly and
The flue system must be installed and terminated in accordance with
the recommendations of BS 5440
art 1.
Terminal Position Min Distance
A1 Directly below an opening, air brick, opening windows etc. 300mm
B1 Above an opening, air brick, opening window etc. 300mm
C1 Horizontally to an opening, air brick, opening window etc. 300mm
D Below gutters, soil pipes or drain pipes 75mm
E Below eaves 200mm
F Below balconies or car port roof (lowest point) 200mm
G From a vertical drain pipe or soil pipe 150mm
H From an internal or external corner 300mm
I Above ground, roof or balcony 300mm
J From a surface facing the terminal 600mm
K From a terminal facing the terminal 1200mm
L From an opening in the car port not
(e.g. door, window) into the dwelling recommended
M Vertically from a terminal on the same wall 1,500mm
N Horizontally from a terminal on the same wall 300mm
P From a vertical structure on the roof *
Q Above intersection with roof *
1 In addition, the terminal should not be nearer than 150 mm (fanned draught) to an opening in the
building fabric formed for the purpose of accommodating a built-in element such as a window frame.
* See instructions supplied with vertical flue kits
spaced such that there is a gap of 50mm between the end of the
terminal and the guard.
3. In certain weather conditions, a white plume of condensation will
be emitted from the flue terminal and siting where this could be a
nuisance, i.e. near security lighting, should be avoided.
4. The air inlet/outlet duct and the terminal of the boiler must not be
closer than 25mm to any combustible material. Detailed
recommendations on protection of combustible materials are given
in BS 5440:1.