Posted: Tue Feb 21, 2006 1:15 pm Post Subject: Cooker Circuit |
 |
|
I have a cooker rated at 11.4 KW. (2 ovens + 4 ring hob)
It has a blanking plate (rating unsure)
It has Cooker switch + socket (rating unsure)
The cable from the Consumer unit is 4mm2 and breaker in the consumer unit is rated at 32Amp.
Are the cable and breaker correctly rated within regulations ?
(I have had no problems with it so far.) |
|
Qedelec

Joined: 22 Jun 2005 Posts: 1141 Location: Birmingham, United Kingdom Thanked: 0 times
|
Posted: Tue Feb 21, 2006 1:25 pm Post Subject: |
 |
|
4mm, 32A, ok. 11.4Kw will take 49.5A on full load, diversity give 10A + 30% f.l. + 5A for a socket.
What do you think?
Personally I would prefer to see a 6mm cable. __________________ "Shock me again and I'm gonna turn you off"
Life's a beach. |
|
plugwash

Joined: 28 Mar 2004 Posts: 6931 Location: United Kingdom Thanked: 16 times
|
Posted: Tue Feb 21, 2006 9:03 pm Post Subject: |
 |
|
as long as there is no thermal insulation anywhere near that cable it should be just about ok. |
|
andy

Joined: 14 Sep 2004 Posts: 3972 Location: United Kingdom Thanked: 0 times
|
Posted: Tue Feb 21, 2006 9:05 pm Post Subject: |
 |
|
cable will be protected, but dont upgrade MCB if the 32A trips |
|