Does anybody know why I have hot water coming out my cold water taps in my bathroom? (The kitchen is ok). The water is also really hot.

I turned the hot water supply off about a week ago to replace a tap and now this has happened. Any idea how to fix it?

(I can also hear the water in my hot water tank boiling! Can this be related as it never used to do this?)
 
Sponsored Links
Some details of type of system would help.

You could have a failed thermostat on an immersion heater causing hot cylinder to boil. Switch of immersion heater to check.

Have you a cold water storage tank in loft. Feel it. Is it cold?
 
I have a tank in the loft and it is hot!

I have a potterton suprima 50L boiler if that helps.

Any ideas?
 
Could be failed cylinder stat or motorised valve allowing the water in the cylinder to boil over back into the cold water storage tank, thus making hot water at hot tap boiling and tank in loft hot. kitchen cold taps ok because fed from cold water main. Bathroom cold taps sound like they are low pressure so are fed from the tank in the loft which as you have described is now boiling hot instead of cold.
Lee
 
Sponsored Links
lcgs said:
Could be failed cylinder stat or motorised valve allowing the water in the cylinder to boil
How would the cylinder water "boil" if the boiler temperature was limited to say 80°C? The boiling of the cylinder water must be due to a failed stat in the immersion heater, which has been left switched on (as jobloggs has already said).
 
Thanks to all who gave their advise...I changed the thermostat on the immersion heater and hey presto...its all back to normal again.

Thanks again... :D
 
Good! The new type stats are much safer than the oldies.
 
In view of the dangers of failure of plastic storage cisterns may I suggest that if yours is plastic that you carefully inspect it all round to ensure that it has not deformed as a result of being heated up!


Tony
 
Hi,

It's my first post here and I could really do with some advice. I have exactly the same problem with hot water coming out of my cold water taps. The water is also boiling in the tank in the loft.

Reading the advice here I've changed the thermostat on the cylinder tank (and set the new one to 60 degrees)but its still doing the same thing (water boiling etc).

When I touch a piece of exposed metal on the tank where the thermostat is clamped on, it actually fells quite cool, so I'm not surprised it keeps asking for water to be heated. Could there be an air bubble in the tank causing this and if so how do I remove it?

I've switched off the immersion heater while this problem exists to prevent damage etc...

Any help would be greatly appreciated!

thanks
 
DO NOT RUN BOTH the boiler and the immersion as this will cause the overheating you describe
make sure that you and your family are not sleeping under the tanks in the loft until this is checked by a very competent engineer.
 
I've changed the thermostat on the cylinder tank (and set the new one to 60 degrees)but its still doing the same thing (water boiling etc).

Do you mean that you have changed the thermostat that is strapped to the outside of the cylinder?

If you have, you have changed the wrong one. The thermostat that controls the immersion heater is under the cover of the element itself (where the supply wires go in)

Isolate the elec. supply to the immersion element, and remove the element cover/cap. Inside you will see a part with a small dial and numbers on. Remove the wires from it, withdraw it from the element, and replace with one of the same type.
 
Hi,

Reading the advice here I've changed the thermostat on the cylinder tank (and set the new one to 60 degrees)but its still doing the same thing (water boiling etc).

thanks

There are TWO thermostats on your cylinder. You have changed one of them and probably not the one causing the problem.

No. 1 thermostat is strapped to your cylinder and controls when the boiler comes on and off to heat the water. I think you have changed this.

No. 2 is built into your immersion heater (is likely under a metal cap so you cannot see it). An immersion heater is an electrical device that protrudes, stick-like, into the top of your cylinder. Probably it is this device's thermostat that has failed and is boiling the water (when your immersion is switched on it keeps heating and heating until the water boils and rises into the loft tank).
 