More Showers

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
drunkenengineer

from United Kingdom

Joined: 29 Nov 2006
Posts: 2
Location: Wight,
United Kingdom
Thanked: 0 times

PostPosted: Wed Nov 29, 2006 10:32 am    Post Subject:
More Showers
Reply with quote Thanks

I currently have a Gainsborough RE600 shower (rating unknown) and intend replacing it with a Triton 9.5kW shower. The cable is 4mm.
Is this a problem? I think the RE600 is 9.5 but am not sure.
By the way, I'm a clanky type, not a greeny!
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Nov 29, 2006 11:22 am    Post Subject:
Reply with quote Thanks

4mm²????? icon_eek.gif icon_eek.gif icon_eek.gif

Do me a favour. Open the shower switch up with the power off, and tell me what you see.

50p says its full of melted plastic and the switch no longer operates. If it isn't you've been very lucky indeed.

Dont use the shower again until you've replaced it with at least 6mm². However, since you're replacing the cable, you might as well go for 10mm².

4mm² will carry 37A IIRC, if run in free space. Your shower is 41 amps (ish)
Back to top
 Alert Moderators
scousespark

from United Kingdom

Joined: 18 Jan 2006
Posts: 338
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Wed Nov 29, 2006 12:13 pm    Post Subject:
Reply with quote Thanks

the RE600 is 8.5Kw, so 4mm is okay but you need to upgrade for a 9.5Kw shower. As crafy said, 10mm should be okay - unless you have a long run or the cable is affected by external factors (eg run through insulation)
Back to top
 Alert Moderators
drunkenengineer

from United Kingdom

Joined: 29 Nov 2006
Posts: 2
Location: Wight,
United Kingdom
Thanked: 0 times

PostPosted: Thu Nov 30, 2006 11:39 am    Post Subject:
Reply with quote Thanks

Thanks to both
Didn't know the RE600 is 8.5 (lost the paperwork). Ill get a new cable run in.
Crafty, 50p please.
DE
Back to top
 Alert Moderators
WF100

from United Kingdom

Joined: 09 Aug 2007
Posts: 1
Location: Surrey,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 09, 2007 12:38 pm    Post Subject:
Voltage Drops
Reply with quote Thanks

Crafty wrote:
4mm²????? icon_eek.gif icon_eek.gif icon_eek.gif

Do me a favour. Open the shower switch up with the power off, and tell me what you see.

50p says its full of melted plastic and the switch no longer operates. If it isn't you've been very lucky indeed.

Dont use the shower again until you've replaced it with at least 6mm². However, since you're replacing the cable, you might as well go for 10mm².

4mm² will carry 37A IIRC, if run in free space. Your shower is 41 amps (ish)


icon_question.gif Hi Guys, I am not an electrician, but doesn't the current draw go up as the voltage goes down? i.e. if the voltage dropped to say 220V(I have seen this many times) the cable will need to carry nearly 39 amps.
So I am assuming that 4mm should not really be used???
Any thoughts???? icon_question.gif
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4540
Location: United Kingdom
Thanked: 10 times

PostPosted: Thu Aug 09, 2007 12:59 pm    Post Subject:
Re: Voltage Drops
Reply with quote Thanks

WF100 wrote:

icon_question.gif Hi Guys, I am not an electrician, but doesn't the current draw go up as the voltage goes down? i.e. if the voltage dropped to say 220V(I have seen this many times) the cable will need to carry nearly 39 amps.


if the voltage goes down, then you need to increase the current *in order to maintain a constant power* (Power = Voltage x current), in a resistive load this doesn't happen, the current actually reduces as well (Current = voltage / Resistance),

9.5kw shower on 240v will take 9500/240 = 39.58A and has a resistance of 240/39.58 = 6.06 ohms

Put the same shower on 230v and the resistance is still 6.06 (its about the only thing thats constant-ish here), which means it'll draw 230/6.06 = 37.95 Amps, which gives it a power of 37.95 x 230 = 8.73kw (the change in power is in proportion the the change in voltage squared - [ P=V²/R])

Regardless of which, neither 4mm² nor WF100 would do! (I wouldn't put it past some though!)
Back to top
 Alert Moderators
FatGit

from United Kingdom

Joined: 29 Jun 2007
Posts: 117
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 09, 2007 1:05 pm    Post Subject:
Reply with quote Thanks

I remember once being told by a drip that they always use 6mm2 cable on a shower as it is easier to work with icon_eek.gif
He tried to use it on mine until I said he was putting in 10mm2 and I watched him do it.
Back to top
 Alert Moderators
CallEdsFirst

from United Kingdom

Joined: 17 Apr 2006
Posts: 355
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 09, 2007 2:29 pm    Post Subject:
Re: Voltage Drops
Reply with quote Thanks

Adam_151 wrote:
neither 4mm² nor WF100 would do! (I wouldn't put it past some though!)


Wasn't there a picture not so long ago of a socket wired in coax???? icon_eek.gif icon_lol.gif
Back to top
 Alert Moderators
bernardgreen

from United Kingdom

Joined: 03 Nov 2006
Posts: 3610
Location: Bedfordshire,
United Kingdom
Thanked: 22 times

PostPosted: Thu Aug 09, 2007 2:36 pm    Post Subject:
Reply with quote Thanks

Or bind the cable to the cold water pipe, cools the cable and pre-heats the water......

That is a JOKE..... DO NOT do it.
Back to top
 Alert Moderators
SUNRAY

from United Kingdom

Joined: 28 Jul 2009
Posts: 204
Location: Kent,
United Kingdom
Thanked: 1 time

PostPosted: Tue Jul 28, 2009 11:26 pm    Post Subject:
Reply with quote Thanks

bernardgreen wrote:
Or bind the cable to the cold water pipe, cools the cable and pre-heats the water......

That is a JOKE..... DO NOT do it.


Sadly seen it done and frequently

Also seen cable run INSIDE the water pipe to a shower
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue Jul 28, 2009 11:44 pm    Post Subject:
Re: Voltage Drops
Reply with quote Thanks

CallEdsFirst wrote:
Adam_151 wrote:
neither 4mm² nor WF100 would do! (I wouldn't put it past some though!)


Wasn't there a picture not so long ago of a socket wired in coax???? icon_eek.gif icon_lol.gif


Might've been mine... icon_eek.gif


__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Goldberg

from United Kingdom

Joined: 30 Jun 2009
Posts: 1211
Location: London,
United Kingdom
Thanked: 44 times

PostPosted: Wed Jul 29, 2009 12:04 am    Post Subject:
Reply with quote Thanks

SUNRAY wrote:
bernardgreen wrote:
Or bind the cable to the cold water pipe, cools the cable and pre-heats the water......

That is a JOKE..... DO NOT do it.

Sadly seen it done and frequently

I think you haven't.

SUNRAY wrote:
Also seen cable run INSIDE the water pipe to a shower

I'm sure you haven't.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21989
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Jul 29, 2009 12:07 am    Post Subject:
Reply with quote Thanks

SUNRAY wrote:
Also seen cable run INSIDE the water pipe to a shower

How would that work?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Goldberg

from United Kingdom

Joined: 30 Jun 2009
Posts: 1211
Location: London,
United Kingdom
Thanked: 44 times

PostPosted: Wed Jul 29, 2009 12:12 am    Post Subject:
Reply with quote Thanks

SUNRAY

from United Kingdom

Joined: 28 Jul 2009 just to wind people up
Posts: 1 useless contribution
Location: Kent,
United Kingdom
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21989
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Jul 29, 2009 12:19 am    Post Subject:
Reply with quote Thanks

Ah - that's a difference between you and I.

I see absolutely no point in mincing around with euphemisms - the meaning is clear and doesn't change, so what's the point in putting lipstick on a pig? Use the L word....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
how to wire 2 electric showers on the same circuit 11 860 Fri Aug 17, 2007 8:41 pm
Renew showers kw?? 3 340 Sun Jul 22, 2007 11:08 am
Showers! 6mm T&E cable to be used for shower 6 860 Sun Aug 19, 2007 10:11 am
2 electric showers 2 300 Fri Aug 24, 2007 11:18 am
mira showers 6 320 Mon Dec 10, 2007 6:12 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.