Flushing toilet causes prolonged vibration / noise in pipes

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
vverman

from United Kingdom

Joined: 13 Apr 2007
Posts: 5
Location: United Kingdom

PostPosted: Fri Apr 13, 2007 3:30 pm Reply with quote

Hi,

I hope someone can advise. I'm using this website for the first time. We have just moved into our first home.

I'll follow the format I have seen some others use:

1) Boiler

STRATA 38 wall mounted ultra high efficiency condensing boiler. The booklet says 'Model 38 boiler & the 38/46 Combi'

2) Problem

There are 3 toilets in the house (1 downstairs, one in main bathroom and one to the en-suite). When the toilet is flushed in the main bathroom, the pipes make a long , loud prolonged noise. When turning on the basin tap I noticed that the noise stops but as soon as I turn of the tap, the pipe vibrations/noise continues (in total when flushing the noise lasts for 30 seconds or so). Notably this happens from the main toilet when flushing but also when using the basin in the en-suite there is some noise although not as bad. A friend suggested bleeding all radiators, from upstairs, going downstairs (as the boiler is in the kitchen). I did this last night but hasn't made much difference. In the main bathroom, when flushing the toilet the loud noise from the pipes seems to be contained within that bathroom, can feel vibration under the floor.

We really need to address this quickly, I am obviously concerned. Prior to buying the house we had a plumber check this out, he must have just turned on a few taps and confirmed that there wasn't a problem. Flushing the toilet is causing this moreso. Before I call out another plumber, would appreciate your feedack and advice. Thank you in advance.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
nickso

from United Kingdom

Joined: 30 Oct 2006
Posts: 6373
Location: United Kingdom
Thanked: 236 times

PostPosted: Fri Apr 13, 2007 3:53 pm Reply with quote

noise is most likely from a valve on the mains water or the pipe could be loose under the floor and vibrating under load......could be the toilet but i would try to move the mains stopcock fully open as a first guess as it may just be the blade inside it vibrating.....worth a try
Back to top
 Alert Moderators
weareleeds

from United Kingdom

Joined: 13 Dec 2005
Posts: 664
Location: Yorkshire,
United Kingdom
Thanked: 2 times

PostPosted: Fri Apr 13, 2007 4:46 pm Reply with quote

May also be faulty ballcock or float valve on toilet
Back to top
 Alert Moderators
wonderb0y

from United Kingdom

Joined: 25 Jan 2007
Posts: 240
Location: United Kingdom
Thanked: 1 time

PostPosted: Fri Apr 13, 2007 4:59 pm Reply with quote

Quote:
A friend suggested bleeding all radiators, from upstairs, going downstairs
icon_eek.gif

i wonder why that didn't make a differance icon_rolleyes.gif

i'd go with above try the float valve first
Back to top
 Alert Moderators
vverman

from United Kingdom

Joined: 13 Apr 2007
Posts: 5
Location: United Kingdom

PostPosted: Sun Apr 15, 2007 8:58 pm Reply with quote

Thank you all for your feedback, I will revert later in the week! V.
Back to top
 Alert Moderators
BoxBasher

from United Kingdom

Joined: 01 Nov 2006
Posts: 998
Location: United Kingdom
Thanked: 2 times

PostPosted: Sun Apr 15, 2007 10:32 pm Reply with quote

nickso wrote:
i would try to move the mains stopcock fully open


And then back one quarter turn so it doesn't seize in the open position.

weareleeds wrote:
May also be faulty ballcock or float valve on toilet

Likely culprit
Back to top
 Alert Moderators
vverman

from United Kingdom

Joined: 13 Apr 2007
Posts: 5
Location: United Kingdom

PostPosted: Mon Apr 16, 2007 12:10 pm Reply with quote

nickso / box - thanks very much for the info.

I hope one of these options will rectify it...would I be able to email you at a person email address to understand things a little better (rather than bore others)! Thanks.
Back to top
 Alert Moderators
BoxBasher

from United Kingdom

Joined: 01 Nov 2006
Posts: 998
Location: United Kingdom
Thanked: 2 times

PostPosted: Mon Apr 16, 2007 12:28 pm Reply with quote

vverman wrote:
would I be able to email you at a person email address to understand things a little better (rather than bore others)! Thanks.


Feel free to keep it public...

... that way others can benefit from the info and add their own opinions/experiences.
Back to top
 Alert Moderators
tomtom82

from United Kingdom

Joined: 21 Nov 2006
Posts: 19
Location: Hull,
United Kingdom

PostPosted: Mon Apr 16, 2007 7:40 pm Reply with quote

n.b. im not a plumber but i had a very simmilar problem with my new toilet causing all the pipeing/boiler to vibrate very loudly.

the plumber eventually found a piece of grit from the new installation in the toilet mechanism which was causing tap slam or water hammer or what ever he called it. good news it was very easy to fix!
Back to top
 Alert Moderators
vverman

from United Kingdom

Joined: 13 Apr 2007
Posts: 5
Location: United Kingdom

PostPosted: Tue Apr 17, 2007 11:14 am Reply with quote

tomtom, Great tip, thanks very much. What I’ll do is shut the stop valve to the toilet in question and then give it a flush to see if the noise persists. If it doesn’t, I believe this indicates that the ballcock (fill valve) is faulty and then I will need to replace this. This is according to the replies I have received so far and from further searches for information on-line. If there is any such grit visible I’ll now clean this up and open up the stop valve and try flushing again to see if the pipes start vibrating and humming again. If they do, then I hope it’s just the ballcock / fill valve.

If I do need to replace the ballcock / fillvalve, can anyone suggest the best place to buy these? From what I’ve read it’s important to get exactly the same make/type (apparently it should stated on the fill valve itself). I would probably try Wickes / B&Q…if someone suggests another large store is better choice first off, please advise.

Thanks again.
Back to top
 Alert Moderators
BoxBasher

from United Kingdom

Joined: 01 Nov 2006
Posts: 998
Location: United Kingdom
Thanked: 2 times

PostPosted: Tue Apr 17, 2007 1:16 pm Reply with quote

Try a proper plumbers merchant as opposed to a shed. They will be able to give you good advice.

Getting an exact match doesn't matter all that much. Just make sure that if it's a side entry you get side entry, bottom entry ditto.
Back to top
 Alert Moderators
vverman

from United Kingdom

Joined: 13 Apr 2007
Posts: 5
Location: United Kingdom

PostPosted: Tue Apr 17, 2007 2:02 pm Reply with quote

Box, thanks for the reply. Based on the above comments, should I purchase both a ‘ballcock’ and ‘float valve’ (or are they part of the same thing?). I’m getting a little confused with the terminology.

Is ‘float-valve’ the same as ‘fill valve’?

Isn’t ballcock just another way of referring to the ‘fill valve’?

Perhaps I’m confusing myself …based on the problem I’ve mentioned and the advice given by others please confirm which part(s) I should be purchasing…

Thank you again.
Back to top
 Alert Moderators
lewisv6

from United Kingdom

Joined: 31 Jul 2009
Posts: 2
Location: Lancashire,
United Kingdom

PostPosted: Fri Jul 31, 2009 3:31 pm Reply with quote

always go for the ballcock first water inlet gear turn off supply of water dismantle it and clean reassemble put water back on if still there replace it easy and cheap to do
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 18752
Location: Bath,
United Kingdom
Thanked: 1496 times

PostPosted: Fri Jul 31, 2009 3:40 pm Reply with quote

Just get the caretaker, maintenance, Gardener to change or service the plastic ballvalve and the problem will be no more. icon_rolleyes.gif
Back to top
 Alert Moderators
lagunaglen

from United Kingdom

Joined: 14 Nov 2007
Posts: 425
Location: Yorkshire,
United Kingdom
Thanked: 2 times

PostPosted: Fri Jul 31, 2009 4:23 pm Reply with quote

ditto doitall,just disassemble the inlet valve,clean and reassemble ,often if there has been any work on the mains in the street it can cause sand to enter and cause minor problems.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Prolonged buzzing noise in rising main when tank nearly full 5 80 Tue Oct 04, 2011 11:16 am
vibration noise transmitting through heating pipes 2 880 Thu Dec 11, 2008 11:47 am
vibration in water pipes after replacing a toilet valve 2 560 Wed Jun 02, 2010 12:51 pm
vibration noise when boiler switches off 6 1100 Tue Mar 25, 2008 9:15 pm
Telford Tempest unvented cylinder resonance/vibration noise 27 5920 Sat Apr 30, 2011 6:42 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.