PostPosted: Tue Jun 05, 2007 8:10 pm    Post Subject:
new cooker . faulty?
Reply with quote Thanks

my husband has just installed a brand new cooker but the cooker box keeps tripping out every time you turn the cooker box on
any ideas why ? is it the wiring or perhaps a fault with the new cooker
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 8:17 pm    Post Subject:
Reply with quote Thanks

What is a cooker box? Could you give some more info regarding the rating of the cooker, the rating of the fuse/MCB, the size of the cable feeding the cooker and any other information that might help us to help you.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Tue Jun 05, 2007 8:20 pm    Post Subject:
Reply with quote Thanks

The thing that keeps tripping. What exactly is written on it? Any chance of a photo?

__________________
I downlights
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4939
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Tue Jun 05, 2007 10:07 pm    Post Subject:
Reply with quote Thanks

And can we have a photo of the thing that is tripping as well icon_lol.gif

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 10:24 pm    Post Subject:
Reply with quote Thanks

its a brand new indesit kd3c1w cooker
hubby bought 3 differnt types of cable in case he was uing the wrong one
but it trips the main panel ( cooker fuse in the fuse box flip switch type )with all the differnt types of cable ( hes tried them all )
unfortunatly the instrctions for the cooker dont state which cable should be used !
you want me to take a photo of the fuse box ?

the cooker box its wired to is just a standard box with an extra socket and lil lights to show whats turned on

i really dont know a thing about electrics !

the only thing the instrctions say re the cable is
min req type ho5rr-f
section 3x4mm2
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 10:35 pm    Post Subject:
Reply with quote Thanks

ive rung an electrician whos offerd to come out in the morning for a £70 call out charge . i'm a little worried he may try to rip me off though ) im dissabled and hubby will be at work, so i feel a bit vulnerable )
watching to much house of horrors and watchdog perhaps ?
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Tue Jun 05, 2007 10:39 pm    Post Subject:
Reply with quote Thanks

You could have had all the help you needed from the forum - when did you book him! icon_eek.gif
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 10:41 pm    Post Subject:
Reply with quote Thanks

i havent yet ,, he siad if i still needed him to call him back in the morning and he will be round within an hour

i expleined best i could the problem and asked about how much his raetes ect were ( as i dont keep much cash in the house , so would have to send someone to the bank for me if it was over £50 , i didnt tell him this )
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 10:54 pm    Post Subject:
Reply with quote Thanks

davy_owen_88 wrote:
What is a cooker box? Could you give some more info regarding the rating of the cooker, the rating of the fuse/MCB, the size of the cable feeding the cooker and any other information that might help us to help you.


not sure what rating is ?

we have 3 types of cable here . hubby bought all the differnt ones the store had just in case

tech charcteristics of cooker just say max oven power absorbtion
1950 w voltage 240 ~50/60hz
ill check the fuse box to see if it says anything on the fuse that trips
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Tue Jun 05, 2007 10:56 pm    Post Subject:
Reply with quote Thanks

buttonbabe wrote:
it trips the main panel ( cooker fuse in the fuse box flip switch type )with all the differnt types of cable ( hes tried them all )
unfortunatly the instrctions for the cooker dont state which cable should be used !
you want me to take a photo of the fuse box ?

Not if it's a difficult thing to do, but could you answer the following question...

RF Lighting wrote:
The thing that keeps tripping. What exactly is written on it?


Also, at the moment of tripping, are any of the cooker controls on? If not, then get your husband to disconnect the cooker from the rear of the cooker switch (in the kitchen), and see if the circuit still trips.

Clearly he should do this only with the cooker circuit isolated at the consumer unit (aka fuse box) by moving the breaker switch into the 'off' position.
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 11:13 pm    Post Subject:
Reply with quote Thanks

ive taken a photo and affer dragging myself around the floor withba torch managed to see what was writton on the fuse switch

hager
mt132 450632(then a tiny 6 )
b32 230-400 v
in a box it says 6000 with a smaller box underneath that says 3

hubbys gone to work ( long distance lorry driver ) whe wont be back for a few days so .. im handling this alone


Last edited by buttonbabe on Tue Jun 05, 2007 11:14 pm, edited 1 time in total
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 11:13 pm    Post Subject:
Reply with quote Thanks

After reading the manual it gives the following ratings:

Front left: 1200W
Rear left: 1700W
Rear right: 1200W
Front right: 1700W
Oven: 1950W

So about 32A FL.

Since you have a 32A MCB that points to a wiring fault or a dodgy cooker. Have a check over his wiring (make sure the electricity supply is isolated before you touch anything). Make sure the bare earth conductor is sleeved and that there are no stray strands loose in the back box.
Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 11:20 pm    Post Subject:
Reply with quote Thanks

Back to top
 Alert Moderators
buttonbabe

from United Kingdom

Joined: 05 Jun 2007
Posts: 13
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Jun 05, 2007 11:21 pm    Post Subject:
Reply with quote Thanks

davy_owen_88 wrote:
After reading the manual it gives the following ratings:

Front left: 1200W
Rear left: 1700W
Rear right: 1200W
Front right: 1700W
Oven: 1950W

So about 32A FL.

Since you have a 32A MCB that points to a wiring fault or a dodgy cooker. Have a check over his wiring (make sure the electricity supply is isolated before you touch anything). Make sure the bare earth conductor is sleeved and that there are no stray strands loose in the back box.


anyone fancy walking me through this by phone icon_cry.gif lol

the trip fuse is on off position so is the cooker box switch .. safe to look ?
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Tue Jun 05, 2007 11:24 pm    Post Subject:
Reply with quote Thanks

buttonbabe, I can't help but be concerned at your apparent vulnerability.

Can you do any of the following:

a) Do without the cooker until your husband returns;
b) Find an electrically competent friend who can come and help;
c) Find a tradesperson who's been recommended to you by someone you know and trust.

icon_question.gif

If the answer is "no" to all of these, then I reckon there's people on the forum who'd be willing to help. I'm not that far away from you myself.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
New cooker fitted,electrical problem or faulty product? 8 420 Wed Feb 27, 2008 8:15 pm
Faulty wiring at electric cooker switch? 16 1060 Tue Jul 06, 2004 4:46 pm
faulty timer programmer !!! 6 420 Thu Jun 29, 2006 8:07 am
Faulty circuit? 24 1060 Sat Aug 05, 2006 9:06 pm
Faulty Consumer unit? 8 580 Sat Sep 02, 2006 5:32 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.