  1. C

    Controlling a radiator zone with underfloor heating

    Yes, a little late from me. 2 zone valves a must. Have a look at the requirements for an auto bypass valve for the pump overrun.
  2. C

    Controlling a radiator zone with underfloor heating

    Your expectations are correct. The boiler should be fed by a permanent live, neutral and earth from a fused spur. (if no heat is called for the boiler should still be on, not firing but on) A live, neutral and earth to the wiring center must also be taken from the spur. The wiring could have...
  3. C

    Controlling a radiator zone with underfloor heating

    Hi Andy Its sounds like the room stat has been wired directly into the boiler as apposed to across the switched live. Does the central heating go off if the room stat is satisfied but the timer remains on. What type of boiler do you have?
  4. C

    my address is [email protected]. drop me a mail and I can send it to you, thanks...

    my address is [email protected]. drop me a mail and I can send it to you, thanks, Collyplumb
  5. C

    Pressure Vessel Location and Testing

    I can send you the manual. How do I get your email address? without us all receiving stuff from all over the web! if there is a metal strip covering only the rear 1/3 of the top of the boiler then this can be removed without exposing the HE.
  6. C

    Pressure Vessel Location and Testing

    Is there any space to get your head over the top and look down the back of the heat exchanger?
  7. C

    Pressure Vessel Location and Testing

    Hi, I have checked boiler manual and it says the expansion vessel sits behind the heat-exchanger. The only way I can see access if from the top of the boiler looking down behind the boiler. The worcester boschs have access from the top but I have not seen the Icon "live".
  8. C

    Is my boiler underpowered?

    Sounds like you have already tried to balance the system... I will read the posts better next time. :oops:
  9. C

    Is my boiler underpowered?

    Hi, I am not a regular on here so the others may come back with something better but.. Have you tried balancing the system? This means turning the lockshield valves of the radiators that are getting hot down to create resistance (not the Thermostatic Rad Valves) thus causing the pump to push...
  10. C

    Rads getting hot when hw is called

    OK but if this was the case then would water not continually run out the drain when only HW is circ with all the rads shut of. this would indicate the link.
  11. C

    Rads getting hot when hw is called

    right. the rads are getting warm from alt ends. L/S when HW call. TRV when CH call. 18 inches away stays cold. so it points to reverse. cool. but i have shut all rads and drained CH flow down. drain still open and i have can blow air through ch flow side. all while HW circulation is on.
  12. C

    Rads getting hot when hw is called

    I think you may be right. I'll give it a go. pretty much exausted all else. thanks for the help dave. sam you to. thanks.
  13. C

    Rads getting hot when hw is called

    I copied theirs but did go over it a couple of times to make sure it added up.
  14. C

    Rads getting hot when hw is called

    Hmm i have not had a very close look at cyl stat wiring. it is working well though. ie. turn, click, on.. turn, click, off ?? thanks though for sticking with me with this
Back