  1. D

    Valliant Boiler ecotech 832- Heating Partial Load

    Interesting .... I will try various modes / setting when the opportunity to log and compare results. This may well not be until around Christmas. Easy to do is dropping the feed temperature to 55C as set now as this will push deeper into condensing mode with a dT of 8 - 10C. I tried once...
  2. D

    Valliant Boiler ecotech 832- Heating Partial Load

    With the feed at around 60C the return in the pipes certainly is not around 45C. I've got probes taped on the pipes in the house before they split to different places. I keep meaning to look for some lagging / wadding to put over them but relatively they show dT is under 10C.
  3. D

    New Boiler slow to heat radiators

    I wonder overall how accurate the sensors are. Temperature ought to be within a degree or so but might the others have a wider tolerance? If I remember I can borrow a temperature probe from work one evening and put into the running tap outlet. There ought not to be a big loss at 10l/min after...
  4. D

    Vaillant Frost / Freezing Protection Statement

    The boiler is in the garage attached to the house on the single brick rear wall. The pipes run at roof level on the joists ... see the thread I started.
  5. D

    New Boiler slow to heat radiators

    Back in time I had a higher flow but while no means then to know actual rates it was noticeably reduced when the first water meter was fitted. The boiler DHW demand is set to 50C. A spot check of boiler readings while running a bath showed the maximum DHW flow rate is 10.5 l/min and the target...
  6. D

    Valliant Boiler ecotech 832- Heating Partial Load

    With D.170 set to 3 ( which is dT mode) D.171 is hidden. To confirm my other settings D.172 is set to 15 D.173 is set to 100 mbar D.174 is set to 400mbar Heating output temperature is set to 60C A spot check when D.040 output temperature 60C and D.041 return temperature 51C showed D.015 22% and...
  7. D

    New Boiler slow to heat radiators

    This would have add complexity. The combination of 2 channel timer, cylinder thermostat, room thermostat and frost thermostat near boiler simply told the boiler to run if any demand then a separate module set the valve position based on room heating only, hot water cylinder heating only or both...
  8. D

    Vaillant Frost / Freezing Protection Statement

    .... logically it should be but all the Vaillant internal 12C protection thermostat does is circulate water within the boiler. Fine for the heating circuit but even if this ran continuously since no flow in cold water feed or tap hot water outlet pipes these could still be frozen solid. The...
  9. D

    Valliant Boiler ecotech 832- Heating Partial Load

    I am only presuming this as unless you can tell me where there is not a readout of the actual dP. As I interpret D.171 is a dP target value setting.
  10. D

    New Boiler slow to heat radiators

    I only found this out after having my basic 12kW boiler, hot water cylinder and Y-plan 3-position valve replaced by a combination boiler. For the old system I set the timer so the cylinder heating and radiator heating did not start at the same time so heating circuit always had the full boiler...
  11. D

    Vaillant Frost / Freezing Protection Statement

    Vaillant could very explicitly state some like ' The integral frost / freezing protection does not protect any external pipes '. If I was designing a boiler controller I would at least include the option to circulate water through the heating circuit if the boiler detected either the feed or...
  12. D

    Valliant Boiler ecotech 832- Heating Partial Load

    D.170 is set to 3 D.172 is set to 15 D.173 is set to 100 mbar, lowest as recall if try to set lower it rolls over to 400mbar. I need to check D.174 but 99% not changed so 400mbar ' which presumably will cause the pump to ramp up and down to give the desired dT ( temperature spread) ' .... so...
  13. D

    Valliant Boiler ecotech 832- Heating Partial Load

    Taking your second pair of readings with 60C boiler output while a 10C dT gives a greater heat output as I understand with 50C return the boiler will only be just be into the condensing zone while at 20C dT it will be well into the zone so will, or at least should be, more efficient. This does...
  14. D

    Vaillant Frost / Freezing Protection Statement

    The manual for my Vaillant Ecotec Plus 832 states that if the internal temperature drops to 12C frost protection will be activated but, to me anyway, it is not clear exactly what the protection is so I contacted Vaillant. Below is their response for reference:- The frost protection cycle will...
  15. D

    Valliant Boiler ecotech 832- Heating Partial Load

    dP or dT mode then the settings are Dxxx codes. The explanation of the modes is in the manual, for mine section 10.3.5 then 10.3.6 - 10.3.8 explain the pressure and the pump. For mine right at the end which I presume is intentional so you access by scrolling back from D000 not going right...