Recent content by Dereekoo

  1. D

    Cracks under Steel Beam

    What is the span of the beam between the supports What is the size of the beam What is the span of the roof between the beam and the inner beam What is the size of the joists supporting the roof and their spacing I assume the roof between the inner beam and outer beam is just a flat bit of roof...
  2. D

    Cracks under Steel Beam

    Trumps a builder
  3. D

    Cracks under Steel Beam

    And of course if you are Eurocode slanted 1.35 and 1.5 spring to mind
  4. D

    Cracks under Steel Beam

    no that would then be 2.24
  5. D

    Cracks under Steel Beam

    Factor of Safety
  6. D

    Cracks under Steel Beam

    Of course its all down to actual calcs and FoS ,not just this is what we always do, 100, 200, 300, would you fret putting a 10m spanning beam if it had no load on it resting on a 50 x 50 angle bolted to a column??
  7. D

    Stock market dealing

    Whats a G wagon is it like a G string
  8. D

    Building over our water supply pipe?

    Yes it can, unfortunately its downstream of the dig zone If he is going to build over their supply pipe he needs to talk to them or do it on the fly
  9. D

    Cracks under Steel Beam

    . Indeed not, remove the load and the beam would spring back to its original shape
  10. D

    Cracks under Steel Beam

    .
  11. D

    Cracks under Steel Beam

    All beams deflect under load , 1/360 or 1/300 span is the general max figure used in BS standards but can be tighter depending on the circumstances i.e. say above a glass partition (extreme case). At 10m the deflection could be 33mm which would be unacceptable in your case and hopefully the...
  12. D

    Building over our water supply pipe?

    OK just making sure that the supply through the field/your property is WC responsibility and as such you are liable to adhere to whatever conditions they dictate
  13. D

    Cracks under Steel Beam

    Possibly due to lintels have a stated SWL and this puts any bearing pressure with the usual specified 150 bearing within the capacity of even soft brickwork and BC know this, not fact ,just an hypotheses.
  14. D

    Cracks under Steel Beam

    NHBC state minimum of 100mm but at the end of the day actual bearing should be confirmed by load calculations
  15. D

    Cracks under Steel Beam

    Because the local bearing stress does not need to be reduced to an acceptable level by using padstones at a guess?